Application of Part R to buildings
90(1) and 90(2)NI-wide·Technical Booklet R Access to and Use of Buildings
Subject to paragraphs (2), (3) and (4) this Part shall apply to any building or part of a building. This Part shall not apply to— (a) any garage or outbuilding associated with a dwelling; (b) any par
dwellingnon-domesticaccessaccessibilityAccess and use of buildings
91NI-wide·Technical Booklet R Access to and Use of Buildings
Reasonable provision shall be made for people to have access to, into, within and to use a building and its facilities: Provided that in a dwelling this requirement shall be limited to the entrance st
dwellingnon-domesticaccessaccessibilityAccess to extensions
92NI-wide·Technical Booklet R Access to and Use of Buildings
Reasonable provision shall be made for independent access to an extension to a building.
dwellingnon-domesticaccessSanitary accommodation in extensions
93NI-wide·Technical Booklet R Access to and Use of Buildings
Where sanitary accommodation is provided in a building, reasonable provision shall be made for the provision of suitable sanitary accommodation in any extension to the building.
dwellingnon-domesticaccessPerformance to satisfy Part R regulations 91-94
0.1NI-wide·Technical Booklet R Access to and Use of Buildings
It is the view of the Department that the requirements of Part R will be met by making reasonable provision to ensure that buildings are accessible and usable. In buildings other than dwellings, peop
accessaccessibilitydwellingnon-domesticAccess routes and parking for non-domestic buildings
0.2NI-wide·Technical Booklet R Access to and Use of Buildings
The guidance in Section 2 is to ensure a suitable and convenient means of access to a building for people from the boundary and from car parking provided on site. Provisions are also given for uncont
accessnon-domesticexternal-spaceBuilding entrances for non-domestic buildings
0.3NI-wide·Technical Booklet R Access to and Use of Buildings
The guidance in Section 3 is to assist people to be able to identify the building entrance and use it to enter the building easily, conveniently and without the risk of injury.
accessnon-domesticCirculation within buildings
0.4NI-wide·Technical Booklet R Access to and Use of Buildings
The guidance in Section 4 is to facilitate the movement of people within a building both within a storey (horizontal circulation) and between storeys (vertical circulation).
accessnon-domesticAccess to and use of building facilities
0.5NI-wide·Technical Booklet R Access to and Use of Buildings
The guidance in Section 5 is to ensure that people have access to and use of all the facilities provided in a building.
accessaccessibilitynon-domesticSection 6: Sanitary accommodation and facilities
0.6NI-wide·Technical Booklet R Access to and Use of Buildings
The guidance in Section 6 is to ensure that sanitary accommodation and associated sanitary facilities provided in a building, are no less available for people with a disability than for non-disabled p
accessibilitynon-domesticpublic-buildingScope of Technical Booklet R
1.2NI-wide·Technical Booklet R Access to and Use of Buildings
The scope of this Technical Booklet is to give provisions for generic solutions to the more common building scenarios to enable people to – (a) get access to a building; (b) get into a building; (c) m
accessaccessibilitydwellingnon-domesticScope of access provisions for buildings other than dwellings
1.3NI-wide·Technical Booklet R Access to and Use of Buildings
The provisions for access to and use of a building are for the benefit of people who are customers or visitors to the building or who work in it.
non-domesticaccessExtensions - approach, entry and sanitary accommodation
1.4NI-wide·Technical Booklet R Access to and Use of Buildings
An extension should be treated in the same manner as a new building. The extension should – (a) be independently approached and entered from the boundary and from car parking within this boundary; or
non-domesticaccessaccessibilityAlterations - maintenance of accessibility
1.5NI-wide·Technical Booklet R Access to and Use of Buildings
When a building is altered the alterations must comply with the requirements of Regulation 91 in Part R. The building, including access to it from the boundary and from on site car parking, where prov
non-domesticaccessaccessibilityMaterial change of use - hotels, institutions, places of assembly, shops
1.6NI-wide·Technical Booklet R Access to and Use of Buildings
When a building undergoes a material change of use so that it is used as a hotel or boarding house, an institution, a place of assembly or recreation, or a shop it should be treated in the same manner
non-domesticcommercialpublic-buildingaccessaccessibilityScope and relationship to fire safety and Part H
1.7NI-wide·Technical Booklet R Access to and Use of Buildings
Part R is limited to matters of access to, into, within, and use of a building. It does not extend to means of escape for a person with a disability in the event of fire, for which reference should be
non-domesticaccessfire-safetystairsrampsAccess statements for extensions and material changes of use
1.10NI-wide·Technical Booklet R Access to and Use of Buildings
In the case of extensions and material changes of use of buildings other than dwellings, and particularly in the case of protected buildings, such a statement will allow an applicant to identify any c
non-domesticaccessaccessibilityconservationSection heading for buildings other than dwellings
NI-wide·Technical Booklet R Access to and Use of Buildings
Buildings other than dwellings
non-domesticaccessaccessibilityGeneral principles for accessible approach to buildings
2.1NI-wide·Technical Booklet R Access to and Use of Buildings
As far as possible, the means of access from the point of entrance at the boundary and from car parking designated for people with a disability which is provided within the boundary, to the principal
non-domesticaccessaccessibilityLevel approach requirement for buildings
2.2NI-wide·Technical Booklet R Access to and Use of Buildings
The means of access to a building should be by a level approach complying with paragraph 2.8 to 2.12. However, where site constraints necessitate that all or any part of the means of access to or betw
non-domesticaccessrampsaccessibilityProvision of complementary steps with ramps
2.3NI-wide·Technical Booklet R Access to and Use of Buildings
As ramps are not necessarily suitable and convenient for all people it is beneficial to have steps as well as a ramp. For example, some people who can walk but have restricted mobility find it more di
non-domesticaccessrampsstairsaccessibilityAlternative means of access for high-rise ramped approaches
2.4NI-wide·Technical Booklet R Access to and Use of Buildings
If the total rise of a ramped approach is too high, it can be unacceptably tiring for wheelchair users and some people with walking difficulties, even if a number of rest landings are provided. Theref
non-domesticaccessrampsaccessibilityPrincipal and alternative entrances
3.1NI-wide·Technical Booklet R Access to and Use of Buildings
A principal entrance(s) and where provided, one entrance which is specifically for members of staff, and any associated lobby, should be accessible. However, where the space outside the principal or s
non-domesticaccessaccessibilityAccessible entrance design and identification
3.2NI-wide·Technical Booklet R Access to and Use of Buildings
Accessible entrances should be clearly sign-posted and easily recognisable. Any structural elements, for example supports for a canopy, are useful in identifying the entrance, but should not present a
non-domesticaccessaccessibilityWayfinding and signage for accessible entrances
3.3NI-wide·Technical Booklet R Access to and Use of Buildings
An accessible entrance should be clearly indicated (e.g. by signs incorporating the International Symbol of Access), from – (a) the point of entrance at the boundary; (b) suitable car parking which is
non-domesticaccessaccessibilityAccess area requirements at entrances
3.4NI-wide·Technical Booklet R Access to and Use of Buildings
An accessible entrance should – (a) be readily apparent (e.g. distinguishable, through suitable visual contrast from that of the adjacent elements of the building); and (b) have an access area – (i) t
non-domesticaccessaccessibilityWeather protection at entrance doors
3.5NI-wide·Technical Booklet R Access to and Use of Buildings
When manually operated entrance doors are installed, the area immediately in front of the entrance doors should, where it is practicable, be protected from inclement weather. This will assist people w
non-domesticaccessaccessibilityEntrance communication system requirements
3.6NI-wide·Technical Booklet R Access to and Use of Buildings
Where an entrance communication system is installed, it should have both video and audio communication to assist people with hearing loss or people who cannot speak.
accessaccessibilitynon-domesticpublic-buildingAccessible entrance doorway threshold levels
3.10NI-wide·Technical Booklet R Access to and Use of Buildings
An accessible entrance doorway should have a threshold which is level. However, where required due to site location (e.g. to prevent the ingress of moisture), a threshold may contain one or more upsta
accessaccessibilitydwellingnon-domesticDoor projection into access routes
3.11NI-wide·Technical Booklet R Access to and Use of Buildings
A door to an accessible entrance should not project, when open, into an adjacent access route, unless that portion of the door which projects into the access route is protected by a suitable barrier.
accessaccessibilitydwellingnon-domesticManually operated entrance door opening force
3.12NI-wide·Technical Booklet R Access to and Use of Buildings
Self-closing devices on manually operated non-powered swing doors can create difficulties for many people who have limited upper body strength, are pushing prams or are carrying heavy objects. The for
accessaccessibilitydwellingnon-domesticDoor handle reach and grip space for wheelchair users
3.12NI-wide·Technical Booklet R Access to and Use of Buildings
A space alongside the leading edge of a door, on the pull side, will enable a wheelchair user to reach and grip the door handle, then open the door without releasing hold on the handle and without the
accessaccessibilitydwellingnon-domesticDoor furniture operability and visibility
3.12NI-wide·Technical Booklet R Access to and Use of Buildings
Door furniture on manually operated non-powered doors should be easy to operate by people with limited manual dexterity, and be readily apparent to assist visually impaired people.
accessaccessibilitydwellingnon-domesticEffective clear width of doorway measurement
3.12 (Diagram 3.1)NI-wide·Technical Booklet R Access to and Use of Buildings
effective clear width when door opens more than 90o effective clear width when door opens to 90o not less than 300 mm (unless door is power operated and activated in accordance with para 3.17) measure
accessaccessibilitydwellingnon-domesticRevolving doors accessibility requirements
3.16NI-wide·Technical Booklet R Access to and Use of Buildings
Revolving doors are not considered accessible. They create particular difficulties, and risk of injury, for people with assistance dogs, visually impaired people or those with mobility problems and fo
accessaccessibilitynon-domesticpublic-buildingPower operated entrance door activation methods
3.17NI-wide·Technical Booklet R Access to and Use of Buildings
A power operated entrance door should have a sliding, swinging or folding action that is activated – (a) manually by a push pad, electronic card, coded entry, or by remote activation; or (b) automatic
accessaccessibilitynon-domesticpublic-buildingManual controls for powered entrance doors
3.18NI-wide·Technical Booklet R Access to and Use of Buildings
Any manual controls to operate a powered entrance door should comply with the requirements of paragraph 5.40 and 5.44(g) (see Diagram 5.8(b)).
accessaccessibilitynon-domesticpublic-buildingPower operated swinging entrance door signage
3.19NI-wide·Technical Booklet R Access to and Use of Buildings
Where a power operated entrance door has a swing action, indication of its operation and direction of swing should be provided to the side that the door opens towards.
accessaccessibilitynon-domesticpublic-buildingAutomatic activation device detection zone positioning
3.20NI-wide·Technical Booklet R Access to and Use of Buildings
Where a power operated entrance door has an automatic activation device, it should be positioned so that the edge of the detection zone, where activation is initiated, is 1400 mm from – (a) the door,
accessaccessibilitynon-domesticpublic-buildingGeneral requirements for circulation within buildings
4.1NI-wide·Technical Booklet R Access to and Use of Buildings
In a building there should be sufficient space for manoeuvring, convenient ways of travelling from one storey to another and the inclusion of features to help people move safely and conveniently throu
non-domesticaccessaccessibilityCorridor and passageway width requirements
4.2NI-wide·Technical Booklet R Access to and Use of Buildings
Corridors and passageways need to be wide enough to allow people with assistance dogs, buggies, people carrying cases, etc., to pass others on the access route. Wheelchair users should also have acces
non-domesticaccessaccessibilityHorizontal circulation and level changes
4.3NI-wide·Technical Booklet R Access to and Use of Buildings
Horizontal circulation within a storey should be level or contain a gradient in the direction of travel less steep than 1 in 20, or by means of a ramp or ramps and landings. Ramps are not necessarily
non-domesticaccessaccessibilityrampsMinimum unobstructed width of corridors and passageways
4.4NI-wide·Technical Booklet R Access to and Use of Buildings
A corridor or passageway should have an unobstructed width of not less than 1200 mm. Minor projections (e.g. skirtings, architraves, etc.) may be ignored. However, where a projection into the corridor
non-domesticaccessaccessibilityPassing places in long corridors and passageways
4.5NI-wide·Technical Booklet R Access to and Use of Buildings
Where a corridor or passageway is more than 50 m in length and has an unobstructed width of less than 1800 mm, it should have passing places spaced at not more than 50 m. Every passing place should be
non-domesticaccessaccessibilityFloor surface requirements for corridors and passageways
4.6NI-wide·Technical Booklet R Access to and Use of Buildings
The floor of a corridor or passageway should – (a) have a surface that has a suitable slip resistance; and (b) be level, or contain a gradient in the direction of travel less steep than 1 in 20. Howev
non-domesticaccessaccessibilityrampsVisibility of doors for visually impaired people
4.12NI-wide·Technical Booklet R Access to and Use of Buildings
The presence of doors, whether open or closed, should be apparent to visually impaired people through the careful choice of colour and material for the door and its surroundings. For example, when a d
accessibilitynon-domesticDoor width for passage
4.12NI-wide·Technical Booklet R Access to and Use of Buildings
Once open, doors should be wide enough to allow unrestricted passage for a variety of users, including wheelchair users.
accessibilitynon-domesticEffective clear width of internal doors in new buildings
4.13NI-wide·Technical Booklet R Access to and Use of Buildings
The effective clear width of a doorway is interrelated to the width of the circulation route and the direction of approach to the doorway. An internal door should contain a leaf, which provides an eff
accessibilitynon-domesticEffective clear width for altered buildings or material change of use
4.14NI-wide·Technical Booklet R Access to and Use of Buildings
Where a building is to be altered or undergo a material change of use and the provisions of paragraph 4.13 cannot be achieved, an internal door may contain a leaf which provides an effective clear wid
accessibilitynon-domesticManually operated internal door requirements
4.15NI-wide·Technical Booklet R Access to and Use of Buildings
When an internal door is designed and constructed to be manually operated it should – (a) comply with the provisions of paragraph 3.13 in relation to opening forces; (b) where the door is fitted with
accessibilitynon-domestic