Section 6: Sanitary accommodation and facilities
0.6NI-wide·Technical Booklet R Access to and Use of Buildings
The guidance in Section 6 is to ensure that sanitary accommodation and associated sanitary facilities provided in a building, are no less available for people with a disability than for non-disabled p
accessibilitynon-domesticpublic-buildingMaterial change of use - hotels, institutions, places of assembly, shops
1.6NI-wide·Technical Booklet R Access to and Use of Buildings
When a building undergoes a material change of use so that it is used as a hotel or boarding house, an institution, a place of assembly or recreation, or a shop it should be treated in the same manner
non-domesticcommercialpublic-buildingaccessaccessibilityEntrance communication system requirements
3.6NI-wide·Technical Booklet R Access to and Use of Buildings
Where an entrance communication system is installed, it should have both video and audio communication to assist people with hearing loss or people who cannot speak.
accessaccessibilitynon-domesticpublic-buildingRevolving doors accessibility requirements
3.16NI-wide·Technical Booklet R Access to and Use of Buildings
Revolving doors are not considered accessible. They create particular difficulties, and risk of injury, for people with assistance dogs, visually impaired people or those with mobility problems and fo
accessaccessibilitynon-domesticpublic-buildingPower operated entrance door activation methods
3.17NI-wide·Technical Booklet R Access to and Use of Buildings
A power operated entrance door should have a sliding, swinging or folding action that is activated – (a) manually by a push pad, electronic card, coded entry, or by remote activation; or (b) automatic
accessaccessibilitynon-domesticpublic-buildingManual controls for powered entrance doors
3.18NI-wide·Technical Booklet R Access to and Use of Buildings
Any manual controls to operate a powered entrance door should comply with the requirements of paragraph 5.40 and 5.44(g) (see Diagram 5.8(b)).
accessaccessibilitynon-domesticpublic-buildingPower operated swinging entrance door signage
3.19NI-wide·Technical Booklet R Access to and Use of Buildings
Where a power operated entrance door has a swing action, indication of its operation and direction of swing should be provided to the side that the door opens towards.
accessaccessibilitynon-domesticpublic-buildingAutomatic activation device detection zone positioning
3.20NI-wide·Technical Booklet R Access to and Use of Buildings
Where a power operated entrance door has an automatic activation device, it should be positioned so that the edge of the detection zone, where activation is initiated, is 1400 mm from – (a) the door,
accessaccessibilitynon-domesticpublic-buildingAudience seating accessibility overview
5.5NI-wide·Technical Booklet R Access to and Use of Buildings
Where permanent or removable seating is provided as part of the design, allowance should be made for people who have a disability to have a choice of seating location at spectator events. Wheelchair u
public-buildingaccessibilitynon-domesticWheelchair spaces in fixed audience seating
5.6NI-wide·Technical Booklet R Access to and Use of Buildings
Where there is fixed audience seating, wheelchair spaces should be provided in accordance with Table 5.1.
public-buildingaccessibilitynon-domesticWheelchair space dimensions and floor requirements
5.7NI-wide·Technical Booklet R Access to and Use of Buildings
A wheelchair space should – (a) have a horizontal floor area; and (b) be not less than 900 mm wide by 1400 mm deep.
public-buildingaccessibilitynon-domesticWheelchair space location and views
5.8NI-wide·Technical Booklet R Access to and Use of Buildings
Wheelchair spaces should be located – (a) in a range of single and double wheelchair spaces, with a standard seat to at least one side of each space or group of spaces; and (b) in such a way as to giv
public-buildingaccessibilitynon-domesticSupport for stepped gangways in terraced seating
5.9NI-wide·Technical Booklet R Access to and Use of Buildings
Any stepped gangway to stepped terrace audience seating, should have a suitable means of providing support to people who have physical difficulty in negotiating changes of level.
public-buildingaccessibilitynon-domesticProvision of wheelchair spaces in audience seating
Table 5.1NI-wide·Technical Booklet R Access to and Use of Buildings
Table 5.1 Provision of wheelchair spaces in audience seating Seating capacity | Minimum provision of wheelchair spaces up to 600 | 1% of total seating capacity (or part thereof) to be permanent wheel
public-buildingaccessibilitynon-domesticArmrests at Wheelchair Spaces
5.10NI-wide·Technical Booklet R Access to and Use of Buildings
Standard fixed seating at the ends of rows and those adjacent to wheelchair spaces should, where they have arm rests, have detachable or lift-up arm rests.
accessibilitypublic-buildingWheelchair Space Depth Requirement
5.10NI-wide·Technical Booklet R Access to and Use of Buildings
the dimension from the front of the wheelchair space to the rear of the access area should be not less than 2000 mm when the area to the back of the wheelchair space gives access to a row of seats and
accessibilitypublic-buildingWheelchair Space Dimensions
5.10NI-wide·Technical Booklet R Access to and Use of Buildings
wheelchair spaces created by removing seating 1400 mm 900 mm
accessibilitypublic-buildingPermanent Wheelchair Space Dimensions and Configuration
Diagram 5.4NI-wide·Technical Booklet R Access to and Use of Buildings
not less than 2300 mm from the front of the wheelchair space where the area to the back of the wheelchair space gives access to a corridor or passageway. permanent wheelchair space not less than 1400
accessaccessibilitypublic-buildingnon-domesticWheelchair Turning Space and Work Surface Heights in Refreshment Facilities
Diagram 5.5NI-wide·Technical Booklet R Access to and Use of Buildings
1500 mm by 1500 mm wheelchair turning space clear knee space under worktop not less than 700 mm above floor level work surface 850 mm above floor level Example 1 - basic refreshment facility Example
accessaccessibilitynon-domesticpublic-buildingClear Knee Space Between Floor Units
Diagram 5.5NI-wide·Technical Booklet R Access to and Use of Buildings
800 mm minimum clear knee space between units
accessaccessibilitynon-domesticpublic-buildingWheelchair accessible changing facilities - General requirements
5.28NI-wide·Technical Booklet R Access to and Use of Buildings
In buildings where changing facilities are provided, some disabled people may require the privacy and convenience of an individual self-contained cubicle or compartment. The self-contained cubicle or
accessibilitynon-domesticpublic-buildingCommunal changing facilities - Wheelchair accessible provision
5.29NI-wide·Technical Booklet R Access to and Use of Buildings
A communal changing facility should have not less than one wheelchair accessible incorporated changing facility. An incorporated changing facility should have the minimum dimensions and arrangement of
accessibilitynon-domesticpublic-buildingSports facilities changing rooms
5.30NI-wide·Technical Booklet R Access to and Use of Buildings
A building for sports facilities should have an individual wheelchair accessible changing room. This is in addition to the provisions of paragraph 5.29.
accessibilitynon-domesticpublic-buildingMultiple wheelchair accessible changing facilities - Transfer layout choice
5.32NI-wide·Technical Booklet R Access to and Use of Buildings
Where there is more than one individual wheelchair accessible changing facility, a mixture of left and right hand transfer layouts should be provided to give the user a choice of transfer sides.
accessibilitynon-domesticpublic-buildingEmergency assistance alarms in wheelchair accessible changing facilities
5.33NI-wide·Technical Booklet R Access to and Use of Buildings
Every individual and incorporated wheelchair accessible changing facility should have – (a) an emergency assistance alarm complying with the provisions of paragraph 6.5; and (b) an emergency assistanc
accessibilitynon-domesticpublic-buildingClear space in front of clothing storage
5.34NI-wide·Technical Booklet R Access to and Use of Buildings
A wheelchair accessible changing facility should have a clear space not less than 1500 mm deep in front of any fixed clothing storage system.
accessibilitynon-domesticpublic-buildingDoor opening direction for emergency access
5.35NI-wide·Technical Booklet R Access to and Use of Buildings
Where a door is provided to a wheelchair accessible changing facility, it should be capable of being opened outwards, from the outside, in the case of an emergency.
accessibilitynon-domesticpublic-buildingmeans-of-escapeFire alarm signals in wheelchair accessible changing facilities
5.36NI-wide·Technical Booklet R Access to and Use of Buildings
Where a fire alarm is provided within a wheelchair accessible changing facility, it should emit both an audible and visual alarm signal.
accessibilityfire-safetynon-domesticpublic-buildingChanging facilities associated with shower facilities
5.37NI-wide·Technical Booklet R Access to and Use of Buildings
A wheelchair accessible changing facility should, where it is associated with a shower facility, have – (a) a floor with a surface that reduces the risk of slipping; and (b) a fixed storage system for
accessibilitynon-domesticpublic-buildingHearing enhancement systems - general
5.47, 5.48NI-wide·Technical Booklet R Access to and Use of Buildings
In order to obtain the full benefit of attending public performances or taking part in meetings/lectures, a person using an electronic hearing device needs to receive a signal that is amplified in bot
public-buildingnon-domesticaccessibilitycommercialHearing enhancement system visibility
5.49NI-wide·Technical Booklet R Access to and Use of Buildings
A hearing enhancement system, provided to comply with the provisions of paragraph 5.48, should be readily apparent to those who require to use it (e.g. indicated by the standard symbol).
public-buildingnon-domesticaccessibilitycommercialHearing enhancement system - electrical interference
5.50NI-wide·Technical Booklet R Access to and Use of Buildings
A hearing enhancement system should not be subject to extraneous electrical interference from any artificial lighting installation.
public-buildingnon-domesticaccessibilitycommercialWater temperature and flow control in educational and public facilities
6.2NI-wide·Technical Booklet R Access to and Use of Buildings
A bath, basin or shower terminal fitting in an educational building, or within a facility provided for the use of the public, should – (a) be supplied with water, through a device or other suitable me
public-buildingnon-domesticaccessibilitysanitary-facilitiesUnisex wheelchair accessible sanitary accommodation at visitor/customer/staff locations
6.12NI-wide·Technical Booklet R Access to and Use of Buildings
At each location where there is sanitary accommodation for visitors, customers or staff, at least one unit of unisex wheelchair accessible sanitary accommodation should be provided. See Diagram 6.1. H
accessibilitynon-domesticpublic-buildingWheelchair accessible unisex sanitary accommodation dimensions and layout
Diagram 6.2NI-wide·Technical Booklet R Access to and Use of Buildings
Wheelchair accessible unisex sanitary accommodation incorporating a standing height washbasin. Plan view showing: not less than 2000 mm (width dimension), not less than 2200 mm (depth dimension), 1400
accessibilitypublic-buildingnon-domesticWater Closet Compartments – Dimensions and Layout
Diagram 6.3NI-wide·Technical Booklet R Access to and Use of Buildings
Diagram 6.3 Water closet compartments (a) WC compartment for ambulant disabled people - Grab rail not less than 500 mm long - Grab rail not less than 500 mm long - Shelf 950 mm above floor level - Cl
accessibilitydwellingnon-domesticpublic-buildingWheelchair accessible unisex sanitary accommodation - design principles
6.16NI-wide·Technical Booklet R Access to and Use of Buildings
Wheelchair users should be able to approach, transfer to and use the sanitary facilities provided within a building. This requires the provision of a wheelchair accessible unisex toilet. The relations
accessibilitynon-domesticpublic-buildingsanitary-facilitiesAmbulant disabled people in separate sex toilet facilities
6.21NI-wide·Technical Booklet R Access to and Use of Buildings
Those who are ambulant disabled people should have the opportunity to use a water closet compartment within any separate sex toilet washroom. The compartment should be fitted with support rails, and i
accessibilitynon-domesticpublic-buildingWheelchair accessible facilities in separate sex sanitary accommodation
6.21NI-wide·Technical Booklet R Access to and Use of Buildings
Where the separate sex sanitary accommodation is accessible by wheelchair users, those users would benefit by having a washbasin and where appropriate, a urinal, installed at a height lower than that
accessibilitynon-domesticpublic-buildingManoeuvring space in standard water closet compartments
6.22NI-wide·Technical Booklet R Access to and Use of Buildings
Within traditional separate sex sanitary accommodation, a water closet compartment not designed as suitable for ambulant disabled people or wheelchair users should, where the door opens into the compa
accessibilitynon-domesticpublic-buildingWater closet pan key dimensions
Diagram 6.4NI-wide·Technical Booklet R Access to and Use of Buildings
not more than 480 mm to top of toilet seat not less than 380 mm or not more than 400 mm not less than 350 mm or not more than 370 mm not less than 240 mm not less than 290 mm
accessibilitynon-domesticpublic-buildingCommunal shower facilities with wheelchair accessible incorporated shower
6.27NI-wide·Technical Booklet R Access to and Use of Buildings
Where a communal shower facility is provided, it should include a wheelchair accessible incorporated shower facility within it. Incorporated shower facilities should have the minimum dimensions and ar
accessibilitynon-domesticpublic-buildingShower facilities in sports activity buildings
6.28NI-wide·Technical Booklet R Access to and Use of Buildings
In addition to the requirements of paragraph 6.27, where there is a shower facility in a building for sports activities, an individual wheelchair accessible shower room should also be provided. See Di
accessibilitynon-domesticpublic-buildingPassenger lift requirements
9.8NI-wide·Technical Booklet R Access to and Use of Buildings
A passenger lift should – (a) have a door or doors which provide a clear opening width of not less than 800 mm; (b) have a car with a width of not less than 900 mm and a depth not less than 1250 mm me
accessibilityaccessnon-domesticflatspublic-buildingFacilities for people with profound and multiple learning disabilities
Appendix ANI-wide·Technical Booklet R Access to and Use of Buildings
The provision of specialist facilities for people with profound and multiple learning disabilities is not a requirement of Building Regulations. However, where it has been decided to provide such a fa
accessibilitynon-domesticpublic-building