Workplace Regulations and application to flats
NI-wide·Technical Booklet K Ventilation
The Workplace (Health, Safety and Welfare) Regulations (Northern Ireland) 1993 (the Workplace Regulations) contain some requirements which affect building design. The main requirements are now covered
flatsdwellingApplication - Buildings not requiring ventilation
64(1)-(2)NI-wide·Technical Booklet K Ventilation
Regulation 65 shall not apply to a building or a space within a building which is used solely for storage or which is otherwise not intended for use by people. Regulations 65 and 66 shall not apply to
ventilationstoragedwellingApplication - New dwellings only
64(4)NI-wide·Technical Booklet K Ventilation
Regulation 67(a) shall apply only to a dwelling being newly erected or created.
ventilationdwellingAdequate means of ventilation
65NI-wide·Technical Booklet K Ventilation
Adequate means of ventilation shall be provided for people in a building. Fixed mechanical ventilation systems and any associated controls shall be tested and commissioned to ensure that the requireme
ventilationnon-domesticdwellingNotification of testing and commissioning
67NI-wide·Technical Booklet K Ventilation
Where this regulation applies, the person carrying out the work, for the purpose of ensuring compliance with regulation 65(2), shall give, not more than 5 days after completion of the testing and comm
ventilationnon-domesticdwellingVentilation of new and existing dwellings
0.4NI-wide·Technical Booklet K Ventilation
The guidance in Section 2 relates to the ventilation of new and existing dwellings. The Section is split into two parts, the first dealing with new dwellings with 3 ventilation methods suggested which
dwellingventilationDefinitions
1.1NI-wide·Technical Booklet K Ventilation
For the purposes of this Technical Booklet the following definitions apply – Air permeability – the air leakage rate in cubic metres per hour per square metre of envelope area (m3/(h.m2)) at a pressu
ventilationdwellingnon-domesticDefinitions: District council, Domestic building, Dwelling
NI-wide·Technical Booklet K Ventilation
District council – is defined in regulation 2 in Part A of the Building Regulations. Domestic building – means a building or part of a building used for residential purposes such as a house, flat, ma
dwellingresidentialDefinitions: Gross internal volume, Habitable room, Infiltration
NI-wide·Technical Booklet K Ventilation
Gross internal volume – the total internal volume of the heated space, including the volume of all furniture, internal walls, internal floors, etc. Habitable room – is a room used for dwelling purpos
dwellingventilationUtility Room
NI-wide·Technical Booklet K Ventilation
Utility room – a room used primarily for laundry purposes which may contain a sink, washing machine, tumble drier or similar moisture producing equipment and which is not entered solely from outside t
ventilationdwellingWet Room
NI-wide·Technical Booklet K Ventilation
Wet room – a room used for domestic activities (e.g. such as cooking, clothes washing and bathing) which give rise to significant production of airborne moisture (e.g. a kitchen, utility room or bathr
ventilationdwellingWhole Building Ventilation (General Ventilation)
NI-wide·Technical Booklet K Ventilation
Whole building ventilation (general ventilation) – nominally continuous ventilation of rooms or spaces at a relatively low rate to dilute and remove pollutants and water vapour not removed by the oper
ventilationdwellingHouse Dust Mite Allergen Control
1.4NI-wide·Technical Booklet K Ventilation
Exposure to house dust mite (HDM) allergens can lead to allergic sensitization and to exacerbation of allergic conditions. The moisture criteria needed to avoid HDM are more complex and demanding than
dwellingventilationAir permeability design options for dwellings
1.6NI-wide·Technical Booklet K Ventilation
The ventilation provisions recommended for new dwellings in this Technical Booklet have been specified according to two standard designs of air permeability – (a) in the default option, the guidance a
dwellingventilationMixed-use buildings with commercial and domestic use
1.7NI-wide·Technical Booklet K Ventilation
Where a building contains both living accommodation and space to be used for commercial purposes (e.g. a workshop or office), the whole building should be treated as a dwelling as long as the commerci
dwellingcommercialventilationDwellings within larger mixed-use buildings
1.8NI-wide·Technical Booklet K Ventilation
When constructing a dwelling as part of a larger building that contains other types of accommodation, Section 2 of this Technical Booklet should be used for guidance in relation to each individual dwe
dwellingventilationVentilation strategy: extract ventilation and whole building air exchange
1.9(a) and (b)NI-wide·Technical Booklet K Ventilation
This Technical Booklet adopts the following strategy (systems that comply with the strategy are described in Sections 2 and 3) – (a) using either intermittent or continuous extract ventilation from ro
dwellingventilationVentilation system types and design flexibility
1.10NI-wide·Technical Booklet K Ventilation
This ventilation strategy can be delivered by a natural ventilation system or a mechanical ventilation system or a combination of both (i.e. "a mixed mode" or "hybrid" ventilation system). For mainly
ventilationdwellingnon-domesticSimple guidance for common situations
1.13NI-wide·Technical Booklet K Ventilation
Simple guidance in the form of ventilator sizes for the whole dwelling is also provided to make it easier for designers to meet building regulation requirements in common situations.
ventilationdwellingAutomatic control of ventilation devices
1.15NI-wide·Technical Booklet K Ventilation
Other types of automatic control may be suitable for regulating ventilation devices (e.g. ventilation fans, dampers and air terminal devices) in dwellings. In such cases, it is important that the devi
ventilationdwellingDemand-controlled ventilation systems
1.16NI-wide·Technical Booklet K Ventilation
Demand-controlled ventilation systems use sensors to detect the level of occupancy, water vapour or other pollutants and adjust the ventilation rate to avoid over-ventilation. In dwellings, humidity-c
dwellingnon-domesticventilationDomestic Ventilation Compliance Guide
1.22NI-wide·Technical Booklet K Ventilation
The Domestic Ventilation Compliance Guide provides guidance on installing ventilation systems in new and existing dwellings. It also has a typical example of an installation checklist for the installe
dwellingventilationAir Flow Testing and Commissioning for Dwellings
1.24NI-wide·Technical Booklet K Ventilation
Where practicable and possible, all mechanical ventilation systems are to be commissioned and the dwelling air flow rates tested and results recorded. With some systems adjustment is not possible beca
dwellingventilationAir Flow Measurement Procedures for Dwellings
1.25NI-wide·Technical Booklet K Ventilation
For dwellings, Sections 2 and 3 of the Domestic Ventilation Compliance Guide contain the procedures for measuring air flow rates and for the commissioning of mechanical systems. The guide also include
dwellingventilationDwelling Owner Information Pack
1.28NI-wide·Technical Booklet K Ventilation
For dwellings, the Domestic Ventilation Compliance Guide lists the documents which should be given to the building owner and includes samples of the inspection checklist and an air flow measurement te
dwellingventilationGeneral - Three Methods of Dwelling Ventilation
2.1NI-wide·Technical Booklet K Ventilation
This Section gives three methods of ventilating dwellings, by – Method 1 – providing the ventilation rates set out in paragraphs 2.5 to 2.7; or Method 2 – following the system guidance set out – (i) f
dwellingventilationMaintenance Access Provision
2.2NI-wide·Technical Booklet K Ventilation
There should be reasonable access provision for maintenance. This should include access for the purpose of changing filters, replacing defective components and cleaning duct work.
dwellingventilationCombustion Appliance Safety and Extract Fans
2.3NI-wide·Technical Booklet K Ventilation
Extract fans and ventilation systems lower the pressure in a building, which can cause the spillage of combustion products from open-flued appliances. This can occur even if the appliance and the fan
dwellingventilationMethod 1 - Performance Requirements for Ventilation Rates
2.4NI-wide·Technical Booklet K Ventilation
The performance will be achieved by providing the air flow rates set out in paragraphs 2.5 to 2.7. The air flow rates specified are for the performance of the complete installation. The performance of
dwellingventilationExtract Ventilation Requirements for Wet Rooms and Kitchens
2.5NI-wide·Technical Booklet K Ventilation
Extract ventilation to outside is required in each kitchen, utility room, bathroom and sanitary accommodation. The extract can be either intermittent or continuously operating. The intermittent rate a
dwellingventilationWhole dwelling ventilation rate
2.6NI-wide·Technical Booklet K Ventilation
The whole dwelling ventilation rate for the supply of air to the habitable rooms in a dwelling should be not less than that specified in Table 2.2.
dwellingventilationRapid ventilation provision in habitable rooms
2.7NI-wide·Technical Booklet K Ventilation
Rapid ventilation provision is required in each habitable room and should be capable of extracting a minimum of four air changes per hour (ach) per room directly to outside. In normal circumstances, o
dwellingventilationExtract ventilation in kitchens, bathrooms and other rooms
2.7NI-wide·Technical Booklet K Ventilation
In other rooms (e.g. kitchens and bathrooms) the mechanical or passive stack extract provisions should provide adequate ventilation, although passive stack ventilation will take longer to purge the ro
dwellingventilationTable 2.2 – Whole dwelling ventilation rates
Table 2.2NI-wide·Technical Booklet K Ventilation
Number of bedrooms in dwelling: 1, 2, 3, 4, 5. Whole dwelling ventilation rate (l/s): 13, 17, 21, 25, 29. Notes: (1) In addition, the minimum ventilation rate should not be less than 0.3 l/s per m² of
dwellingventilationTable 2.1 – Extract ventilation rates
Table 2.1NI-wide·Technical Booklet K Ventilation
Room: Kitchen, Utility room, Bathroom, Sanitary accommodation. Intermittent extract – Minimum rate: Kitchen 30 l/s adjacent to hob or 60 l/s elsewhere; Utility room 30 l/s; Bathroom 15 l/s; Sanitary a
dwellingventilationVentilation Systems for Dwellings Without Basements - Overview
2.8NI-wide·Technical Booklet K Ventilation
The performance required for dwellings without basements could be achieved by following one of the four systems listed in paragraph 2.11. Worked examples for each system are given in Appendix C.
dwellingventilationDesign Air Permeability Guidance
2.9NI-wide·Technical Booklet K Ventilation
For each system, guidance is given for dwellings to cover all design air permeabilities. Therefore, for ventilation purposes, it is not necessary for the as-built permeability to be close to the desig
dwellingventilationAlternative Guidance for High Air Permeability Dwellings
2.10NI-wide·Technical Booklet K Ventilation
In addition to this guidance, for each system, alternative guidance is provided for dwellings with as-built air permeabilities greater than 3 m3/(h.m2) at 50 Pa. It is recommended that this option is
dwellingventilationSystem 1: Background Ventilators and Intermittent Extract Fans
2.11 - System 1NI-wide·Technical Booklet K Ventilation
System 1 – Background ventilators and intermittent extract fans. Guidance on minimum provisions for extract and whole dwelling ventilation is set out in paragraphs 2.12 to 2.40. Note that it includes
dwellingventilationSystem 2: Passive Stack Ventilation
2.11 - System 2NI-wide·Technical Booklet K Ventilation
System 2 – Passive stack ventilation (PSV). Guidance on minimum provisions for extract and whole dwelling ventilation is set out in paragraphs 2.41 to 2.64.
dwellingventilationSystem 3: Continuous Mechanical Extract
2.11 - System 3NI-wide·Technical Booklet K Ventilation
System 3 – Continuous mechanical extract (MEV). Guidance on minimum provisions for extract and whole dwelling ventilation is set out in paragraphs 2.65 to 2.84.
dwellingventilationSystem 4: Continuous Mechanical Supply and Extract with Heat Recovery
2.11 - System 4NI-wide·Technical Booklet K Ventilation
System 4 – Continuous mechanical supply and extract with heat recovery (MVHR). Guidance on minimum provisions for extract and whole dwelling ventilation is set out in paragraphs 2.85 to 2.104.
dwellingventilationVentilation Systems for Dwellings without Basements
Diagram 2.1NI-wide·Technical Booklet K Ventilation
System 1: background ventilators and intermittent extract fans System 2: passive stack ventilation System 3: continuous mechanical extract System 4: continuous mechanical supply and extract with heat
dwellingventilationBackground ventilators sizing for winter
2.12NI-wide·Technical Booklet K Ventilation
The background ventilators have been sized for the winter period. Additional ventilation may be required during warmer months and it has been assumed that the provisions for rapid ventilation (e.g. op
dwellingventilationIntermittent extract rates
2.13NI-wide·Technical Booklet K Ventilation
Intermittent extract rates are given in Table 2.1. For sanitary accommodation only, as an alternative, the rapid ventilation provisions (i.e. Windows) given in Appendix B can be used.
dwellingventilationSingle room heat recovery ventilator as alternative
2.14NI-wide·Technical Booklet K Ventilation
Instead of a conventional intermittently used extract fan, a continuously running single room heat recovery ventilator could be used in wet rooms. It should use the minimum high rate given in Table 2.
dwellingventilationInstallation of intermittent extract fans in wet rooms
2.15NI-wide·Technical Booklet K Ventilation
Intermittent extract fans should be installed in each wet room.
dwellingventilationHeight of extract fan installation
2.16NI-wide·Technical Booklet K Ventilation
Intermittent extract fans other than cooker hoods should be installed as high as is practicable and preferably within 400 mm of the ceiling.
dwellingventilationCooker hood installation height
2.17NI-wide·Technical Booklet K Ventilation
Cooker hoods should be 650 mm to 750 mm above the hob surface (or installed in accordance with the manufacturer's instructions).
dwellingventilationSeparation of fans and background ventilators
2.18NI-wide·Technical Booklet K Ventilation
Where fans and background ventilators are provided in the same room they should be a minimum of 500 mm apart.
dwellingventilation