Technical Booklet K Ventilation·Page 16·1.15
Automatic control of ventilation devices
Automatic controls may be used on ventilation fans, dampers, and air terminals to regulate ventilation based on the need to remove pollutants and water vapour, with manual override requirements for user control.
Other types of automatic control may be suitable for regulating ventilation devices (e.g. ventilation fans, dampers and air terminal devices) in dwellings. In such cases, it is important that the device controls the ventilation air supply and/or extract according to the need for ventilation in the space to remove or dilute indoor pollutants and water vapour. Trickle ventilators with automatic controls should also have manual override, so that the occupant can close the ventilator to avoid draughts and fully open the ventilator to provide maximum air flow when required. For pressure controlled trickle ventilators that are fully open at typical conditions (e.g. 1 Pa pressure difference), only a manual close option is recommended.
Source — /Users/richardhill/Documents/planning-arch-project/data/documents/regional/Technical Booklet K - Ventilation.pdf