Technical Booklet K Ventilation·Page 20·2.3
Combustion Appliance Safety and Extract Fans
Extract fans and ventilation systems can cause depressurisation that risks spillage of combustion products from open-flued appliances. Open-flued combustion appliances must operate safely whether or not fans are running; refer to Part L guidance.
Extract fans and ventilation systems lower the pressure in a building, which can cause the spillage of combustion products from open-flued appliances. This can occur even if the appliance and the fan are in different rooms. Ceiling sweep fans produce air currents and hence local depressurisation which can also cause the spillage of flue gases from open-flued gas appliances or from solid fuel open fires. In buildings where it is intended to install open-flued combustion appliances and extract fans, the combustion appliance should be able to operate safely whether or not the fans are running. Refer to Part L, Combustion appliances and fuel storage systems.
Source — /Users/richardhill/Documents/planning-arch-project/data/documents/regional/Technical Booklet K - Ventilation.pdf