Automatic fire suppression systems
37BNI-wide·Technical Booklet E Fire Safety
A building shall be designed and constructed with a suitable automatic fire suppression system. This regulation applies only to— (a) a building, containing one or more flats, with a storey more than 1
fire-safetyhigh-risehrbflatsAutomatic Fire Suppression Systems - Performance
0.16CNI-wide·Technical Booklet E Fire Safety
It is the view of the Department that the requirements of Regulation 37B in Part E will be met when a suitable automatic fire suppression system is provided where it is necessary. The key characteris
fire-safetyhrbFirefighting lift
NI-wide·Technical Booklet E Fire Safety
Firefighting lift – a lift designed to have additional protection, with controls that enable it to be used under the direct control of the Fire and Rescue Service when fighting a fire.
fire-safetyhrbhigh-riseFirefighting lobby
NI-wide·Technical Booklet E Fire Safety
Firefighting lobby – a protected lobby for providing access from a firefighting stairway to the accommodation area and to any associated firefighting lift.
fire-safetyhrbhigh-risemeans-of-escapeFirefighting shaft
NI-wide·Technical Booklet E Fire Safety
Firefighting shaft – a protected enclosure containing a firefighting stairway, firefighting lobbies and, if provided, a firefighting lift together with its machinery.
fire-safetyhrbhigh-riseFirefighting stairway
NI-wide·Technical Booklet E Fire Safety
Firefighting stairway – a protected stairway communicating with the accommodation area only through a firefighting lobby.
fire-safetymeans-of-escapestairshrbhigh-risePlaces of special fire hazard
NI-wide·Technical Booklet E Fire Safety
Places of special fire hazard – oil-filled transformer and switchgear rooms, boiler rooms, storage space for fuel or other highly flammable substances and rooms housing a fixed internal combustion eng
fire-safetyhrbDefined term: Unprotected area
NI-wide·Technical Booklet E Fire Safety
Unprotected area – in relation to a side or external wall of a building means – (a) a window, door or other opening; (b) any part of the external wall which has less than the relevant fire resistance
fire-safetyhrbhigh-riseAssessment of Fire Performance for Extended Applications
NI-wide·Technical Booklet E Fire Safety
For performance classifications where there is no specific standard for extended application, assessment reports should be produced in accordance with the principles of BS EN 15725 and should include
fire-safetyhrbExternal Wall Materials Classification Requirement
Regulation 23(2)NI-wide·Technical Booklet E Fire Safety
Regulation 23(2) limits components used in or on the external walls of relevant buildings to materials achieving European Classification A2-s1, d0 or Class A1 (see Section 5). Assessments cannot be us
fire-safetyexternal-spacehrbMaterial of Limited Combustibility – European Classification
1.10NI-wide·Technical Booklet E Fire Safety
A material of limited combustibility is under European classification – (a) any material or product classified as non-combustible under paragraph 1.8(a) or (b); or (b) a material or product classified
fire-safetynon-domestichrbStair width calculation example for floors 1-9
2.65(ii)NI-wide·Technical Booklet E Fire Safety
To find the width of the stairs serving floors 1 to 9 – P = 1200/2 = 600, n = 9 From the formula: 600 = 200w + 50 (w - 0.3) (9 - 1) 600 = 200w + (50w - 15) (8) 600 = 200w + 400w - 120 720 = 600w w = 1
stairsmeans-of-escapehrbPhased evacuation design concept
2.66NI-wide·Technical Booklet E Fire Safety
In certain buildings it may be advantageous to design the escape stairways on the concept of phased evacuation. With phased evacuation the first people to be evacuated are those on the floor of the fi
means-of-escapehrbfire-safetyaccessibilityRequirements for phased evacuation buildings
2.66(a)-(g)NI-wide·Technical Booklet E Fire Safety
In such a building, or part of a building – (a) every escape stairway should be approached through a protected lobby or protected corridor at each storey, other than at a top storey consisting exclusi
means-of-escapefire-safetyhrbhigh-risestairsaccessibilityRefuge in a stair with wheelchair space
Diagram 2.12, para. 2.78NI-wide·Technical Booklet E Fire Safety
Diagram 2.12 Refuge in a stair Provision where access to the wheelchair space is counter to the access flow within the stairway
fire-safetymeans-of-escapeaccessibilityhrbhigh-riseRefuge formed by compartmentation in stairway
Diagram 2.13, para. 2.78NI-wide·Technical Booklet E Fire Safety
Diagram 2.13 Refuge formed by compartmentation Storey divided into two refuges by compartment wall (stairways not provided with wheelchair space). Note: Persons occupying the left-hand compartment wou
fire-safetymeans-of-escapehrbhigh-riseExamples of satisfactory refuges
2.78NI-wide·Technical Booklet E Fire Safety
The following are examples of satisfactory refuges – (a) an enclosure such as a protected stairway (see diagram 2.12) or protected lobby, protected corridor or compartment (see diagram 2.13); and (b)
fire-safetymeans-of-escapehrbWheelchair accessible refuge space
2.79NI-wide·Technical Booklet E Fire Safety
Each refuge should provide an area accessible to a wheelchair of at least 900 mm x 1400 mm in which a wheelchair user can await assistance. Where a refuge is in a protected stairway or protected lobby
fire-safetymeans-of-escapeaccessibilityhrbRefuge and evacuation lift signage
2.80NI-wide·Technical Booklet E Fire Safety
Refuges and evacuation lifts should be clearly identified by appropriate signs. Where a refuge is in a lobby or stairway the sign should be accompanied by a blue mandatory sign worded "Refuge - keep c
fire-safetymeans-of-escapehrbEmergency voice communication system for refuges
2.81NI-wide·Technical Booklet E Fire Safety
To facilitate the effective evacuation of people temporarily waiting in each refuge an emergency voice communication system should be provided. It is essential that the occupants of each refuge are ab
fire-safetymeans-of-escapeaccessibilityhrbEvacuation lifts – general provisions
2.82NI-wide·Technical Booklet E Fire Safety
In general, it is not appropriate to use a lift when there is a fire in the building. However, in some circumstances a suitably sited and protected lift containing certain safety features may be used
fire-safetymeans-of-escapehrbFire protection of lift installations
2.83NI-wide·Technical Booklet E Fire Safety
For general provisions relating to the fire protection of lift installations, see paragraphs 2.99 and 2.100.
fire-safetyhrbPressurization systems compatibility with building services
NI-wide·Technical Booklet E Fire Safety
Where a pressurization system is installed in a protected stairway all mechanical ventilation and air conditioning systems in the building should be compatible with it when operating under fire condit
fire-safetymeans-of-escapehrbhigh-riseWaste chutes and storage room requirements
2.102NI-wide·Technical Booklet E Fire Safety
A room used for the storage of waste or containing a waste chute should be – (a) separated from other parts of the building by fire-resisting construction; (b) located outside protected stairways and
fire-safetynon-domestichrbThermoplastic lighting diffusers in fire-protecting or fire-resisting ceilings
3.15NI-wide·Technical Booklet E Fire Safety
A thermoplastic lighting diffuser should not be incorporated in a fire-protecting or fire-resisting ceiling unless it has been satisfactorily tested as part of a luminaire within a ceiling assembly th
fire-safetyhrbLimitations on groups of thermoplastic rooflights and lighting diffusers in suspended ceilings
Diagram 3.1NI-wide·Technical Booklet E Fire Safety
Diagram 3.1 Limitations on groups of Class 3 plastic rooflights and TP(b) thermoplastic rooflights and lighting diffusers in suspended ceilings see para 3.14(b), 3.16(b) and Table 3.2 note (1) and (4)
fire-safetyhrbFire Resistance Test Provisions for Building Elements
Table 4.1NI-wide·Technical Booklet E Fire Safety
Table 4.1 Specific provisions of test for fire resistance of elements of structure and other components of a building Part of building | Minimum provisions when tested to the relevant part of BS 476
fire-safetystructuralhrbTable 4.1: Fire Resistance Test Provisions for Building Elements
Table 4.1NI-wide·Technical Booklet E Fire Safety
Table 4.1 Specific provisions of test for fire resistance of elements of structure and other components of a building (cont'd) Part of building | Minimum provisions when tested to the relevant part o
fire-safetyhrbstructuraldwellingnon-domesticTable 4.3: Limitations of fire-protecting suspended ceilings
Table 4.3NI-wide·Technical Booklet E Fire Safety
Table 4.3 Limitations of fire-protecting suspended ceilings Height of building or separated part (m) | Type of floor | Fire resistance of floor required by Table 4.2 (minutes) | Type of suspended cei
fire-safetyhrbstructuralSuspended ceiling types W, X, Y, Z - Material and classification requirements
Table 4.3 NotesNI-wide·Technical Booklet E Fire Safety
Ceiling type Description W Surface of ceiling exposed to the cavity should be Class 0 or Class 1 (National Class) or Class C-s3,d2 or higher (European Class). X Surface of ceiling exposed to the cavit
fire-safetyhrbFire-protecting suspended ceiling access panel requirements
Table 4.3 NotesNI-wide·Technical Booklet E Fire Safety
Any access panels provided in fire-protecting suspended ceilings of Type Y or Z should be secured in position by releasing devices or screw fixings, and they should be shown to have been tested in the
fire-safetyhrbCavity barriers in rain screen cladding voids
Table 4.6, Item 9NI-wide·Technical Booklet E Fire Safety
Within the void behind the external face of rain screencladding at every floor level, and on the line of compartment walls abutting the external wall, of buildings which have a floor more than 18 m ab
fire-safetyhigh-risehrbFire-resisting ceiling requirements
Diagram 4.7NI-wide·Technical Booklet E Fire Safety
The ceiling should – (a) have at least 30 minutes fire resistance; (b) be imperforate except for an opening described in paragraph 4.42; (c) extend throughout the building or compartment; and (d) not
fire-safetyhrbCavity ceiling surface classification
Diagram 4.7NI-wide·Technical Booklet E Fire Safety
upper ceiling surface – Class 1 (National class) or Class C-s3,d2 (European class) lower ceiling surface – Class 0 (National class) or Class B-s3,d2 or higher (European class)
fire-safetyhrbCorridor enclosure with cavity barriers
Diagram 4.8NI-wide·Technical Booklet E Fire Safety
Alternative arrangements for corridor enclosure: (a) Section showing use of cavity barriers above the corridor enclosure as required by Table 4.6 (b) Alternative arrangement plan showing subdivision o
fire-safetymeans-of-escapehrbFire resistance requirements for flues in compartment walls and floors
Diagram 4.12NI-wide·Technical Booklet E Fire Safety
In all cases flue walls should have a fire resistance of at least one half of that required for the compartment wall or compartment floor and be of non-combustible construction.
fire-safetynon-domestichrbMaterials and Products for High-Rise Buildings
5.4NI-wide·Technical Booklet E Fire Safety
Where a building has a storey the floor of which is 18 m or more above ground level, any insulation material, and any filler material (such as the core materials of metal composite panels, sandwich pa
hrbhigh-risefire-safetyexternal-spaceReaction to fire performance of external surface of walls
Table 5.1ANI-wide·Technical Booklet E Fire Safety
Table 5.1A Reaction to fire performance of external surface of walls Building Type | Building height | Less than 1m from the relevant boundary | 1m or more from the relevant boundary 'Relevant build
fire-safetyhrbhigh-riseexternal-spaceRegulation 23(2) - Materials in External Walls of Relevant Buildings
5.4DNI-wide·Technical Booklet E Fire Safety
Regulation 23(2) applies to any building with a storey at least 18m above ground level and which contains one or more dwellings; an institution; or a room for residential purposes (excluding any room
dwellinghigh-risefire-safetyhrbScope of Regulation 23(2) - Building Types Included
5.4D Note 1NI-wide·Technical Booklet E Fire Safety
The above includes any building with a storey at least 18m above ground level that contains student accommodation, care homes, nursing homes, sheltered housing, hospitals, dormitories in boarding scho
dwellinghigh-risefire-safetyhrbpublic-buildingEuropean Classification Requirement - Class A2-s1, d0 or A1
5.4D Note 2NI-wide·Technical Booklet E Fire Safety
The requirement in Regulation 23(2) is limited to materials achieving European classification Class A2-s1, d0 or Class A1. Therefore materials achieving limited combustibility cannot be deemed to meet
fire-safetyhrbMaterial Change of Use - External Wall Requirements
5.4GNI-wide·Technical Booklet E Fire Safety
Regulation 8 provides that, where the use of a building is changed such that the building becomes a building described in Regulation 23(4), the construction of the external walls, and specified attach
fire-safetyhrbMembranes in External Walls - Minimum Classification
5.4H(a)NI-wide·Technical Booklet E Fire Safety
membranes used as part of the external wall construction should achieve a minimum classification of European Class B-s3, d0;
fire-safetyhrbUnprotected areas in external walls
5.10NI-wide·Technical Booklet E Fire Safety
Any part of an external wall which has less fire resistance than that required by Section 4 should be considered to be an unprotected area. Where an external wall has the appropriate fire resistance
fire-safetyexternal-spacehrbhigh-riseExternal walls 1 m or more from relevant boundary
5.12NI-wide·Technical Booklet E Fire Safety
An external wall situated 1 m or more from any point on its relevant boundary may have unprotected areas provided that their total area does not exceed that given by the most favourable calculation me
fire-safetyexternal-spacehrbTP(a) and TP(b) plastic rooflights – Limitations on use and boundary distance
Table 5.9NI-wide·Technical Booklet E Fire Safety
Table 5.9 TP(a) and TP(b) plastic rooflights – Limitations on use and boundary distance Minimum classification on lower surface (1) | Space which rooflight can serve | Minimum distance (m) from any p
fire-safetyhrbglazingFirefighting Shafts - General Requirements
6.2NI-wide·Technical Booklet E Fire Safety
In low rise buildings without deep basements fire and rescue personnel access requirements will be met by a combination of the normal means of escape in the building and the measures for vehicle acces
fire-safetyhigh-risehrbFirefighting Shafts - When Required
6.3NI-wide·Technical Booklet E Fire Safety
A building should be provided with a firefighting shaft or shafts, to serve all storeys, where – (a) it has a storey more than 18 m above fire and rescue access level; (b) it is a building of Purpose
fire-safetyhigh-risehrbcommercialFirefighting shaft scope - basement and upper storey service requirements
NI-wide·Technical Booklet E Fire Safety
However, a firefighting shaft provided under (a) or (b) need not serve a basement storey unless (c) or (d) applies and similarly a firefighting shaft provided under (c) or (d) need not serve an upper
fire-safetyhrbhigh-risemeans-of-escapeFirefighting shaft components and outlet locations
NI-wide·Technical Booklet E Fire Safety
NOTES: 1. Outlets from a fire main should be located in the firefighting lobby or, in the case of a shaft serving flats, in the firefighting stairway (see Diagram b). 2. Smoke control should be provid
fire-safetyhrbhigh-riseflatsmeans-of-escape