Technical Booklet E Fire Safety·Page 64·2.66(a)-(g)

Requirements for phased evacuation buildings

Buildings using phased evacuation must provide protected lobbies, compartment floors, sprinkler systems (if over 30 m), fire detection and alarm systems, voice alarm systems, and emergency voice communication systems with specifications.

In such a building, or part of a building – (a) every escape stairway should be approached through a protected lobby or protected corridor at each storey, other than at a top storey consisting exclusively of plant rooms; (b) a protected lobby at each storey should be provided to the approach to every lift that is not within the enclosure of a protected stairway other than at a top storey consisting exclusively of plant rooms; (c) every floor should be a compartment floor; (d) an automatic sprinkler system complying with the relevant recommendations of BS 5306-2 or BS EN 12845, should be installed in accordance with Section 8 throughout the building where the building has a storey more than 30 m above ground level; (e) an automatic fire detection and fire alarm system, to BS 5839-1, of at least Category L3 standard, should be installed; (f) a voice alarm system to BS 5839-8 should be installed throughout the building, or part of the building; and (g) an emergency voice communication system to BS 5839-9 should be installed with a master station at fire and rescue access level (see Section 6) and an outstation on every storey.