Technical Booklet E Fire Safety·Page 94·Table 4.1
Table 4.1: Fire Resistance Test Provisions for Building Elements
Specifies minimum fire resistance ratings (in minutes) for various building elements and structures when tested to BS 476 or European standards, covering loadbearing capacity, integrity, and insulation performance.
Table 4.1 Specific provisions of test for fire resistance of elements of structure and other components of a building (cont'd)
Part of building | Minimum provisions when tested to the relevant part of BS 476 (minutes) | Minimum provisions when tested to the relevant European standard (minutes) | Method of exposure
| Loadbearing capacity | Integrity | Insulation | |
10 Firefighting shafts –
(a) construction separating firefighting shafts from remainder of building | 120 | 120 | 120 | REI 120 | From side remote from shaft
(b) construction with a firefighting shaft separating firefighting stairway, firefighting lift shaft and firefighting lobby | 60 | 60 | 60 | REI 60 | From shaft side
| 60 | 60 | 60 | REI 60 | Each side separately
11 Enclosure (which is not a compartment wall or described in item 8) to a –
(a) protected lobby or refuge | 30 | 30 | 30 | REI 30 | Each side separately
(b) protected corridor | 30 | 30 | 30 | REI 30 |
12 Subdivision of a corridor | 30 | 30 | 30 | REI 30 | Each side separately
13 Wall separating an attached or integral garage from a dwellinghouse | 30 | 30 | 30 | REI 30 | From garage side
14 Fire-resisting construction –
(a) in dwellings not described elsewhere | 30 | 30 | 30 | REI 30 | Each side separately
(b) enclosing places of special fire hazard | 30 | 30 | 30 | REI 30 |
(c) between retail areas in a shop and store rooms | 30 | 30 | 30 | REI 30 |
(d) fire-resisting subdivision described in Note (4) to Table 4.6 | 30 | 30 | 30 | REI 30 |