Emergency voice communication system for refuges
An emergency voice communication system must be provided at each refuge to enable occupants to alert others that they need assistance and to receive reassurance that help is coming. The system should comply with BS 5939-9 with a Type B outstation at each refuge, or alternatively use readily operable wireless technology suitable for disabled people.
To facilitate the effective evacuation of people temporarily waiting in each refuge an emergency voice communication system should be provided. It is essential that the occupants of each refuge are able to alert other people that they are in need of assistance and for them to be reassured that their presence in the refuge is known and that assistance will be forthcoming. The emergency voice communication system should either -
a) comply with BS 5939-9 and consist of a Type B outstation at each refuge which communicates with a master station located in the building control room (where provided) or adjacent to the fire alarm panel; or
b) in some buildings, it may be more appropriate to use an alternative approach such as the use of wireless technology. Such technology needs to be readily operated by, and comprehensible to disabled people.