Application of Stair and Ramp Requirements
Regulation 54(2)NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
The requirements of regulation 56 shall only apply where a stair, ladder or a ramp and landings— (a) forms part of the building; (b) that does not form part of the building, is provided to comply with
stairsrampsaccessGeneral requirements for stairs, ramps, guarding and protection from impact
0.1NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Provisions for accessibility to and within a building are given in Part R. Provisions for fire safety are given in Part E. A stair or a ramp and its landings provided – (a) so that people may move to,
stairsrampsfire-safetyaccessSection 2 Overview - Access routes to buildings
2.1NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Section 2 gives guidance on appropriate levels of safety and convenience for all users where a ramp or a ramp and complementary steps are to be provided as an access route or part of an access route t
rampsaccessaccessibilitySection 2 Coverage and scope
2.2NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
This Section is presented as follows – Ramps and complementary steps on access routes to buildings other than dwellings; and Ramps and steps on access routes to dwellings.
rampsaccessaccessibilitydwellingnon-domesticRamps on access routes to non-domestic buildings
2.3NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Ramps on access routes should comply with the provisions given in paragraphs 4.14 to 4.25. See Diagram 2.1. However, where an external ramp has a crossfall, that crossfall should have a maximum gradie
rampsaccessnon-domesticRamped approach requirements
2.13NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A ramped approach should have – (a) a surface which is firm and even; (b) an unobstructed width not less than 900 mm; (c) a ramp or ramps not exceeding – (i) 10 m in length where the slope of the ramp
dwellingaccessrampsStepped approach requirements
2.14NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A stepped approach should have – (a) a flight or flights with an unobstructed width of not less than 900 mm; (b) a rise of not more than 1800 mm in each flight of steps; (c) steps with a uniform rise
dwellingaccessstairsHandrail specifications for stepped approach
2.15NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A stepped approach should have a suitable handrail which – (a) is at a height measured vertically of – (i) 900 mm above the pitch line of a flight of steps; and (ii) 1000 mm above the surface of a lan
dwellingaccessstairsprotection-from-fallingHandrails for private stairs accessing principal storey
3.25NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Notwithstanding the provisions of paragraph 3.24, where a private stair – (a) is part of the circulation route within the entrance storey of a dwelling; or (b) gives access to the circulation route wi
dwellingstairsaccessLanding Requirements
3.36NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A landing should be provided at the top and bottom of every flight. The width of the landing should be not less than the width of the stair. To afford safe passage, the unobstructed length of each lan
stairsaccessSection 4: General - Ramps as means of circulation
4.1NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
This Section gives guidance on appropriate levels of safety and convenience for all users where a ramp is to be provided as a means of circulation within a building.
rampsaccessmeans-of-escapeLandings
4.11NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Landings should be level with an unobstructed length of not less than 1200 mm.
rampsaccessHeadroom
4.12NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Ramps and associated landings should have a clear headroom of not less than 2000 mm over the length and width of the ramp. Headroom is measured vertically from the slope of the ramp and the level of t
rampsaccessHandrails
4.13NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A ramp should have a suitable continuous handrail on each side if the horizontal length of the ramp is more than 2000 mm. Handrails should be at a height between 900 mm and 1000 mm measured vertically
rampsaccessprotection-from-fallingGradients of ramps in buildings other than dwellings
4.14NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Gradients of ramps should be as shallow as practicable as steep gradients may not be safe or convenient for all people. The following provisions apply to a ramp which is not in a dwelling or in a bloc
rampsaccessnon-domesticMaximum length and rise of ramps
4.15NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
The maximum length of a ramp is dependent upon its gradient. Table 4.1 gives the maximum length of a ramp for a given gradient. There may be exceptional circumstances where a different gradient of ram
rampsaccessnon-domesticTable 4.1 Maximum length and rise of ramps
Table 4.1NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Gradient of ramp | Maximum length of ramp (m) | Maximum rise of ramp (mm) 1:20 | 10 | 500 1:19 | 9 | 474 1:18 | 8 | 444 1:17 | 7 | 412 1:16 | 6 | 375 1:15 | 5 | 333 1:14 | 4 | 286 1:13 | 3 | 231 1:12
rampsaccessnon-domesticWidth of ramps
4.16NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A ramp or ramps and landings should have a surface width of not less than 1500 mm. Where a handrail protrudes into the surface width of a ramp by more than 100 mm the surface width should be increased
rampsaccessaccessibilityConstruction of ramps
4.17NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
The surface of a ramp should – (a) be firm; (b) reduce the risk of slipping; and (c) be distinguishable, through suitable visual contrast, from that of its landings. A ramp and its landings should hav
rampsaccessRaised kerbs on ramps
4.18NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A ramp should have a raised kerb on any open side (except where it would obstruct normal use). The raised kerb should – (a) be not less than 100 mm high; and (b) be distinguishable, through suitable v
rampsprotection-from-fallingaccessLanding provision and dimensions for ramps
4.19NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Wheelchair users need adequate space to stop on landings, to open and pass through doors without having to reverse into circulation routes and to avoid the risk of rolling back down slopes. A landing
rampsaccessibilityaccessIntermediate landings for multiple ramps
4.20NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Where the ramped access or circulation route consists of three or more ramps, the intermediate landings between each ramp should have an unobstructed length of not less than 1800 mm and a surface widt
rampsaccessibilityaccessLine of sight on ramps and landing dimensions
4.21NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Where a ramp does not have a clear line of sight between its top and bottom landings, it should be divided into two ramps such that there is a clear line of sight between the intermediate landing and
rampsaccessibilityaccessZones of visibility for doors and gates on main routes
7.1NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A door or gate – (a) across a main route of travel; or (b) which can be pushed open from either side, should have, towards the leading edge of the door leaf, zones of visibility as shown in Diagram 7.
accessprotection-from-fallingnon-domesticVisibility zones for adjacent side panels
7.2NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Any side panel that is more than 450 mm wide and is adjacent to a door or gate, that is required by paragraph 7.1 to have zones of visibility, should also have zones of visibility. See Diagram 7.1.
accessprotection-from-fallingnon-domesticSafety requirements for power-operated pedestrian doors and gates
7.5NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A power operated door or gate designed and constructed for pedestrian use should – (a) incorporate a safety stop or door re-activating device to prevent the door striking a person passing through if t
accessprotection-from-fallingnon-domestic