Section 4: Single family houses, annexes and small single storey buildings
Section 4NI-wide·Technical Booklet D Structure
Single family houses, annexes and small single storey buildings
dwellingstructuralTechnical Booklet D: Structure - Purpose and Status
NI-wide·Technical Booklet D Structure
This Technical Booklet, which takes effect on 31st October 2012, is one of a series that has been prepared by the Department of Finance and Personnel (the Department) for the purpose of providing prac
structuralScope - Regulations Covered
NI-wide·Technical Booklet D Structure
The guidance contained in this Technical Booklet relates only to the requirements of regulations 30 and 31. The work will also have to comply with all other relevant requirements of the Building Regul
structuralMaterials and Workmanship Requirements
regulation 23NI-wide·Technical Booklet D Structure
Any building work which is subject to requirements imposed by Part A of the Building Regulations should be carried out in accordance with regulation 23 of those regulations. Guidance on meeting these
structuralConstruction sequence documentation requirements
5(b)NI-wide·Technical Booklet D Structure
an indication of the proposed construction sequence, if this is not obvious to a competent contractor. This is particularly relevant to refurbishments and new basements to existing buildings.
structuralnon-domesticApplicability to non-domestic clients and projects of all sizes
5NI-wide·Technical Booklet D Structure
Note that these regulations apply to non-domestic clients, designers and contractors no matter what the duration or size of the project.
non-domesticstructuralWorkplace Regulations application to common parts of flats
NI-wide·Technical Booklet D Structure
The Workplace Regulations apply to the common parts of flats and similar buildings if people such as cleaners, wardens and caretakers are employed to work in these common parts. Where the requirements
flatsstructuralStability
Regulation 30NI-wide·Technical Booklet D Structure
A building shall be designed and constructed so that the combined dead, imposed and wind loads are sustained and transmitted to the ground, taking into account the nature of the ground— (a) safely; an
structuralDisproportionate collapse
Regulation 31NI-wide·Technical Booklet D Structure
A building shall be designed and constructed so that in the event of damage occurring to any part of the building, the extent of any resulting collapse will not be disproportionate to the cause of the
structuralRegulation 30 in Part D - Stability Performance
Regulation 30NI-wide·Technical Booklet D Structure
It is the view of the Department that the requirements of regulation 30 in Part D will be met when the structure of a building is designed and constructed — (a) so as to ensure the safety of those peo
structuralSatisfying regulation 30 - Codes and standards for all building types
paragraphs 2.2 to 2.9NI-wide·Technical Booklet D Structure
For all building types, following the recommendations given in the documents listed in paragraphs 2.2 to 2.9 should demonstrate compliance with the requirements of regulation 30 in Part D. However, wh
structuralFurther considerations - Structural safety factors
0.2NI-wide·Technical Booklet D Structure
The safety of a structure depends on the successful combination of design and completed construction, particularly — (a) identification of hazards to which the structure is likely to be subjected and
structuralActions and Dynamic Load Effects
NI-wide·Technical Booklet D Structure
Actions used in calculations should allow for possible dynamic, concentrated and peak load effects that may occur. The design should ensure that the effects of actions do not cause a situation of irre
structuralAlternative Approach for Single Family Houses, Annexes and Small Single Storey Buildings
0.3NI-wide·Technical Booklet D Structure
For a single family house of not more than 3 storeys in height, an annex or a small single storey building, a designer may wish to follow the guidance given in Section 4 of this Technical Booklet to d
dwellingstructuralIntroduction to Section 4 Provisions: Basic Stability Requirements
4ANI-wide·Technical Booklet D Structure
Part 4A of Section 4 provides guidance on the basic requirements for stability.
structuralIntroduction to Section 4 Provisions: Timber Members
4BNI-wide·Technical Booklet D Structure
The guidance in Part 4B of Section 4 is concerned with various timber members. Provisions are given in relation to the strength, loadings, sizes and spacings of those timber members.
structuralIntroduction to Section 4 Provisions: Masonry Walls
4CNI-wide·Technical Booklet D Structure
Part 4C of Section 4 provides guidance on the design of masonry walls. Provisions are given regarding conditions relating to the building, conditions relating to the wall and wall thickness.
structuralIntroduction to Section 4 Provisions: Masonry Chimneys
4DNI-wide·Technical Booklet D Structure
Part 4D of Section 4 provides guidance on the proportions for masonry chimneys above the roof surface.
structuralIntroduction to Section 4 Provisions: Concrete Strip Foundations
4ENI-wide·Technical Booklet D Structure
The guidance in Part 4E of Section 4 is concerned with the design of concrete strip foundations.
structuralRegulation 31: Disproportionate collapse - Performance
Regulation 31NI-wide·Technical Booklet D Structure
It is the view of the Department that the requirements of regulation 31 in Part D will be met when a building is designed and constructed so as to ensure the safety of people in or about the building.
structuralall-building-typesSatisfying Regulation 31 in Part D
Regulation 31NI-wide·Technical Booklet D Structure
For all building types, following the recommendations given in the documents listed in paragraph 2.10 should demonstrate compliance with the requirements of regulation 31 in Part D. Alternatively, fol
structuralall-building-typesIntroduction to provisions in Section 3
Section 3NI-wide·Technical Booklet D Structure
Section 3 gives the procedure to determine the measures required for ensuring that the building is sufficiently robust to sustain a limited extent of damage or failure, depending on the class of the b
structuralGeneral rules for Parts 4B and 4C
1.1NI-wide·Technical Booklet D Structure
The general rules in paragraph 4A.1 should be complied with when using Parts 4B and 4C of Section 4. Sections 3 and 4 may be used independently of each other.
structuralDefinitions - Buttressing wall
1.2NI-wide·Technical Booklet D Structure
Buttressing wall – a wall designed and constructed to afford lateral support to another wall perpendicular to it, support being provided from the base to the top of the wall.
structuralDefinitions - Cavity width
1.2NI-wide·Technical Booklet D Structure
Cavity width – the horizontal distance between the two leaves of a cavity wall.
structuralDefinitions - Dead load
1.2NI-wide·Technical Booklet D Structure
Dead load – the load due to the weight of all walls, permanent partitions, floors, roofs and finishes, including services, and all other permanent construction.
structuralDefinitions - Imposed load
1.2NI-wide·Technical Booklet D Structure
Imposed load – the load assumed to be produced by the intended occupancy or use, including the weight of movable partitions, distributed, concentrated, impact, inertia and snow loads, but excluding wi
structuralDefinitions - Pier
1.2NI-wide·Technical Booklet D Structure
Pier – a member which forms an integral part of a wall, in the form of a thickened section at intervals along the wall so as to afford lateral support to the wall to which it is bonded or securely tie
structuralDefinitions - Spacing
1.2NI-wide·Technical Booklet D Structure
Spacing – the distance between the longitudinal centres of any 2 adjacent timber members of the same type, measured in the plane of floor, ceiling or roof structure of which the members form a part.
structuralSpan Definition
NI-wide·Technical Booklet D Structure
Span – the distance measured along the centre line of a member between the centres of any two adjacent bearings or supports. Note: the spans given in Part 4B of Section 4 for floor joists, rafters, p
structuralSupported Wall Definition
NI-wide·Technical Booklet D Structure
Supported wall – a wall to which lateral support is afforded by a combination of buttressing walls, piers or chimneys acting in conjunction with floor(s) or roof.
structuralWind Load Definition
NI-wide·Technical Booklet D Structure
Wind load – the load due to the effect of wind pressure or suction.
structuralSection 2: Codes and Standards for Structural Design
2.1NI-wide·Technical Booklet D Structure
This Section is relevant to all building types and lists Codes and Standards for structural design and construction which if followed, should demonstrate compliance with the requirements of regulation
structuralall-building-typesLoadings – Eurocode 1
2.2NI-wide·Technical Booklet D Structure
Eurocode 1 - Action on structures BS EN 1991-1-1(1). BS EN 1991-1-3(1). BS EN 1991-1-4(1).
structuralReinforced, Prestressed or Plain Concrete – Eurocode 2
2.3NI-wide·Technical Booklet D Structure
Eurocode 2 - Design of concrete structures BS EN 1992-1-1(1). BS EN 1992-1-2(1).
structuralSteel – Eurocode 3
2.4NI-wide·Technical Booklet D Structure
Eurocode 3 - Design of steel structures BS EN 1993-1-1(1). BS EN 1993-1-2(1). BS EN 1993-1-3(1). BS EN 1993-1-5(1). BS EN 1993-1-8(1). BS EN 1993-1-10(1).
structuralComposite Steel and Concrete – Eurocode 4
2.5NI-wide·Technical Booklet D Structure
Eurocode 4 - Design of composite concrete and steel structures BS EN 1994-1-1(1). BS EN 1994-1-2(1).
structuralTimber - Eurocode 5 Design Standards
2.6NI-wide·Technical Booklet D Structure
BS EN 1995-1-1(1). BS EN 1995-1-2(1). (1) To be read in conjunction with the associated National Annex and BS EN 1990.
structuraltimberMasonry - Eurocode 6 Design Standards
2.7NI-wide·Technical Booklet D Structure
BS EN 1996-1-1(1). BS EN 1996-1-2(1). BS EN 1996-3(1). (1) To be read in conjunction with the associated National Annex and BS EN 1990.
structuralmasonryFoundations - Eurocode 7 Geotechnical Design Standards
2.8NI-wide·Technical Booklet D Structure
BS EN 1997-1(1). (1) To be read in conjunction with the associated National Annex and BS EN 1990.
structuralAluminium - Eurocode 9 Design Standards
2.9NI-wide·Technical Booklet D Structure
BS EN 1999-1-1(1). BS EN 1999-1-2(1). BS EN 1999-1-3(1). (1) To be read in conjunction with the associated National Annex and BS EN 1990.
structuralRobustness and Disproportionate Collapse - Eurocode 1 Standards
2.10NI-wide·Technical Booklet D Structure
BS EN 1991-1-7(1). (1) To be read in conjunction with the associated National Annex and BS EN 1990.
structuralUsing alternative codes and standards to satisfy regulation 30
2.11NI-wide·Technical Booklet D Structure
As an alternative to the codes and standards referenced in paragraphs 2.2 to 2.9, the documents referred to in paragraphs 2.12 to 2.19, which were withdrawn by the British Standards Institution on 31
structuralall-buildingsWithdrawn standards for structural loadings
2.12NI-wide·Technical Booklet D Structure
BS 6399: Part 1 (excluding imposed roof loads). BS 6399: Part 2. BS 6399: Part 3.
structuralWithdrawn standards for reinforced, prestressed or plain concrete
2.13NI-wide·Technical Booklet D Structure
BS 8110: Part 1. BS 8110: Part 2. BS 8110: Part 3.
structuralWithdrawn standards for steel
2.14NI-wide·Technical Booklet D Structure
BS 5950: Part 1. BS 5950: Part 2. BS 5950: Part 5.
structuralWithdrawn standards for composite steel and concrete
2.15NI-wide·Technical Booklet D Structure
BS 5950: Part 3. BS 5950: Part 4.
structuralWithdrawn standards for timber
2.16NI-wide·Technical Booklet D Structure
BS 5268: Part 2. BS 5268: Part 3.
structuralMasonry design standards
2.17NI-wide·Technical Booklet D Structure
BS 5628: Part 1. BS 5628: Part 2. BS 5628: Part 3.
structuralnon-domesticFoundations design standards
2.18NI-wide·Technical Booklet D Structure
BS 8004.
structural