Scope and Application of Technical Booklet H
NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
This Technical Booklet, which takes effect on 31st October 2012, is one of a series that has been prepared by the Department of Finance and Personnel (the Department) for the purpose of providing prac
stairsrampsguardingprotection-from-impactSpecific Regulations Covered
NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
The guidance contained in this Technical Booklet relates only to the requirements of regulations 56, 57, 58, 59 and 60. The work will also have to comply with all other relevant requirements of the Bu
stairsrampsguardingPurpose of Building Regulations
NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
The Building Regulations are made for specific purposes, primarily securing the health, safety, welfare and convenience of people and for the conservation of fuel and power. Standards and technical ap
stairsrampsguardingprotection-from-fallingApplication of Named Standards
NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Where this Technical Booklet makes reference to a named standard, the relevant version of the standard is the one listed in the Appendix. However, if this version has been replaced or updated by the i
stairsrampsguardingprotection-from-fallingUse of Diagrams in Technical Booklet
NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
The diagrams in this Technical Booklet supplement the text. They do not show all the details of construction and are not intended to illustrate compliance with any other requirement of the Building Re
stairsrampsguardingprotection-from-fallingProtected Buildings and Special Consideration
NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
District councils have a duty to take account of the desirability to preserve the character of protected buildings when carrying out their functions under Building Regulations. Therefore, where work i
stairsrampsguardingprotection-from-fallingconservationRelationship to Other Legislation
NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
The provisions of this Technical Booklet relate to the requirements of Building Regulations and do not include measures which may be necessary to meet the requirements of other legislation. Such other
stairsrampsguardingprotection-from-fallingThe Workplace (Health, Safety and Welfare) Regulations (Northern Ireland) 1993
NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
The Workplace (Health, Safety and Welfare) Regulations (Northern Ireland) 1993 (the Workplace Regulations) contain some requirements which affect building design. The main requirements are now covered
stairsrampsguardingprotection-from-fallingnon-domesticWorkplace Regulations Application to Common Parts of Flats
NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
The Workplace Regulations apply to the common parts of flats and similar buildings if people such as cleaners, wardens and caretakers are employed to work in these common parts. Where the requirements
flatsnon-domesticstairsrampsguardingprotection-from-impactPart H Application and Scope
Regulation 54(1)NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Subject to paragraphs (2) to (6), this Part shall apply to any building or part of a building.
stairsrampsguardingprotection-from-fallingApplication of Stair and Ramp Requirements
Regulation 54(2)NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
The requirements of regulation 56 shall only apply where a stair, ladder or a ramp and landings— (a) forms part of the building; (b) that does not form part of the building, is provided to comply with
stairsrampsaccessExceptions to Guarding Requirements
Regulation 54(3)NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
The requirements of regulation 57(1) shall not apply— (a) to the extent that compliance therewith would unreasonably obstruct normal movement to, into, out of or within any building; (b) in relation t
guardingprotection-from-fallingstairsProvision of stairs in multi-storey dwellings
55NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Within every dwelling of more than one storey there shall be provided between such storeys access by means of a stair complying with the relevant provisions in this Part: Provided that nothing in this
dwellingstairsSafety of stairs, ladders, ramps and landings
56NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
In a building or within the boundary of a building a stair, ladder and a ramp and its landings, shall offer reasonable safety to people using them.
stairsrampsGuarding requirements for elevated and open areas
57(1)NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A stair, ladder, ramp, floor, balcony, landing, platform and any roof or other place to which people normally have access (including access for the purpose of maintenance) and a sunken area next to a
stairsrampsprotection-from-fallingguardingGeneral requirements for stairs, ramps, guarding and protection from impact
0.1NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Provisions for accessibility to and within a building are given in Part R. Provisions for fire safety are given in Part E. A stair or a ramp and its landings provided – (a) so that people may move to,
stairsrampsfire-safetyaccessPerformance standard for reasonable safety
0.2NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
It is the view of the Department that the requirements of regulation 56 in Part H will be met when a stair, ladder, ramp and its landings afford reasonable safety to people who use them. As there is a
stairsrampsdwellingnon-domesticpublic-buildingGuidance scope for stairs and ladders
0.4NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
The guidance in Section 3 is concerned with various aspects of the geometry and safety of stairs and certain ladders. This includes common provisions for all stairs and additional provisions for – (a)
stairsdwellingflatsnon-domesticScope of Technical Booklet H
NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Provisions are also given for spiral and helical stairs in a dwelling and stairs and ladders used solely for the purpose of providing access for maintenance in buildings other than dwellings. The guid
stairsrampsdwellingnon-domesticSection 5 Introduction - Provisions for Guarding and Fall Protection
0.6NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
The guidance in Section 5 is concerned with reducing the risk of people falling from a height. This includes provisions for guarding flights, ramps, landings and raised floors. This Section also conta
protection-from-fallingguardingrampsstairsDefinitions
1.1NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
In this Technical Booklet the following definitions apply – Dwelling – has the meaning assigned to it by regulation 2 in Part A of the Building Regulations. Entrance storey – means the storey which
dwellingstairsrampsprotection-from-fallingSurface width definition
NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Surface width – the width of a stair or ramp, measured at the tread of a step or the surface of a ramp, between any enclosing walls, strings, upstands, kerbs or guarding.
stairsrampsprotection-from-fallingTapered tread definition
NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Tapered tread – a tread which has a greater width at one side than at the other and a going which changes at a constant rate throughout its length.
stairsVisual contrast and Light reflectance value
1.2NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Visual contrast is the perception of a difference visually between one element of a building and another by reference to their light reflectance values. Light reflectance value (LRV) is the total qua
stairsrampsaccessibilityvisual-contrastMeasuring rise and going
Diagram 1.1NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Diagram 1.1 Measuring rise and going - showing going measured from nosing to nosing, with details of treads, risers, nosings, and open/closed rise configurations. See paragraphs 1.1, 3.4 and 3.14.
stairsVisually impaired people and changes in level
2.4NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Visually impaired people risk tripping or losing their balance if there is no warning that there is a change in level. Tripping is most hazardous at the head of a flight of steps when a person is desc
accessibilitystairsrampsprotection-from-fallingTread dimensions for people with mobility impairments
2.5NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
People who wear callipers or who have stiffness in hip or knee joints are particularly at risk of tripping or catching their feet beneath nosings. People with a weakness on one side or with a sight im
accessibilitystairsrampsRamped approach with complementary steps layout
2.5NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Where complementary steps and a ramp share a surface containing their respective notional landings, it is preferred that the tactile warning surface be located clear of the ramp landing.
rampsstairsaccessibilityComplementary steps - rise and going dimensions
2.6NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Steps should have a uniform – (a) rise of not less than 150 mm and not more than 170 mm; and (b) going of not less than 280 mm and not more than 425 mm.
stairsComplementary steps - maximum flight length
2.7NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A flight of steps should have not less than 2 rises or more than – (a) 12 rises where the going of each step is less than 350 mm; or (b) 18 rises where the going of each step is 350 mm or more.
stairsComplementary steps - surface width
2.8NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A flight should have a surface width of not less than that given in paragraph 3.32.
stairsComplementary steps - additional guidance
2.9NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Steps should also comply with the guidance given in paragraphs 3.33 to 3.35.
stairsComplementary steps - handrails
2.10NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
To assist a person who is weaker on one side and a visually impaired person, steps should have a suitable continuous handrail on each side complying with the provisions of paragraphs 3.37 to 3.43.
stairsaccessibilityprotection-from-fallingTactile warning surfaces on complementary steps landings
2.11NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
To give advance warning of the change in level, a tactile corduroy surface should be provided on the top and bottom landings of complementary steps. See Diagram 2.2. The size of this surface should be
stairsaccessibilityprotection-from-fallingTactile warning surfaces on intermediate landings
2.12NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Where there is access onto any intermediate landing from other than the complementary steps, a tactile corduroy surface 400 mm deep should be provided in accordance with Diagram 2.3 (b) or (c).
stairsaccessibilityprotection-from-fallingCorduroy tactile warning surface tile specification
Diagram 2.2NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Corduroy tactile warning surface tiles: 20 mm tile depth, 6 mm rib profile, 20 mm rib, 30 mm gap
stairsaccessibilityprotection-from-fallingComplementary steps - tactile warnings requirements
Diagram 2.3NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Diagram 2.3 Complementary steps - tactile warnings (b) external steps showing side access onto intermediate landing and having not less than 800 mm from the access to the top and bottom of flights -
stairsaccessibilityprotection-from-fallingexternal-spaceStepped approach requirements
2.14NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A stepped approach should have – (a) a flight or flights with an unobstructed width of not less than 900 mm; (b) a rise of not more than 1800 mm in each flight of steps; (c) steps with a uniform rise
dwellingaccessstairsHandrail specifications for stepped approach
2.15NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A stepped approach should have a suitable handrail which – (a) is at a height measured vertically of – (i) 900 mm above the pitch line of a flight of steps; and (ii) 1000 mm above the surface of a lan
dwellingaccessstairsprotection-from-fallingExternal Step Profiles
Diagram 2.4NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
External step profiles: minimum 60° angle; tread and riser dimensions 15–25 mm. See para 2.14.
stairsexternal-spaceprotection-from-fallingSection 3: Stairs - General
3.1NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
This Section gives guidance on appropriate levels of safety and convenience for all users where a stair is to be provided so that people can move between levels or storeys in a building. Provisions ar
stairsCommon provisions for private and common stairs in dwellings
3.2NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A private stair or a common stair in a block of dwellings, should comply with the provisions of paragraphs 3.4 to 3.28.
stairsdwellingflatsCommon provisions for other stairs
3.3NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A stair, other than a private stair or a common stair in a block of dwellings, should comply with the provisions of paragraphs 3.4 to 3.11 and 3.29 to 3.43.
stairsnon-domesticPitch of a flight
3.4NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
The pitch of a flight is controlled by limiting the rise and the going. Diagram 3.1 shows how to measure the pitch and what is meant by the pitch line. Diagram 1.1 shows how to measure the rise and go
stairsRise and going relationship formula
3.5NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Subject to paragraph 3.12 the relationship between the dimensions of the rise and going is that twice the rise (R) plus the going (G) i.e. (2R + G) should be between 550 mm and 700 mm. The rise and th
stairsUniform rise and going within a flight
3.6NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
In a flight, the steps should all have the same rise and they should all have the same going.
stairsRise measurement on sloping landings
3.7NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Where the landing of a stair is formed by the ground and slopes across the width of the flight, then the rise of the step should be measured at the mid-point of the width of the flight. See paragraph
stairsLevel treads extending full width
3.8NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Steps should have level treads which extend for the full width of the flight.
stairsMinimum headroom requirement
3.9NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
A stair should have a clear headroom of not less than 2000 mm over its full length and width. Headroom is measured vertically from the pitch line of the flight and the level of the landing. See Diagra
stairsdwellingRise and going dimensions by stair category
Table 3.1NI-wide·Technical Booklet H Stairs Ramps Guarding and Protection from Impact
Table 3.1 Rise and going Category | Rise minimum (mm) | Rise maximum (mm) | Going minimum (mm) | Going maximum (mm) Private stair | 75 | 220* | 220 | — A common stair in a block of dwellings | 75 | 1
stairsdwellingflats