Workplace Regulations and Building Regulations Coverage
NI-wide·Technical Booklet N Drainage
The Workplace (Health, Safety and Welfare) Regulations (Northern Ireland) 1993 (the Workplace Regulations) contain some requirements which affect building design. The main requirements are now covered
flatsnon-domesticaccessCesspool construction requirements
7(2)NI-wide·Technical Booklet N Drainage
A cesspool shall be— (a) of suitable depth to enable it to be emptied completely; (b) properly covered so as to be impervious to surface water and rainwater; (c) fitted with a suitable manhole cover f
drainagenon-domesticdwellingSeptic tank and treatment plant construction requirements
7(3)NI-wide·Technical Booklet N Drainage
Any structure to which paragraph (1) applies other than a cesspool shall be— (a) of suitable depth; (b) of adequate size, having in no case a capacity of less than 2.7 m³; (c) covered or fenced in; (d
drainageseptic-tanktreatment-plantnon-domesticdwellingPerformance Standards for Foul Water Drainage Systems
0.1NI-wide·Technical Booklet N Drainage
It is the view of the Department that the requirements of regulations 80 and 81 will be met if a foul water drainage system – (a) conveys the flow of foul water to a foul water outfall connected to a
drainagenon-domesticdwellingGuidance on Sanitary Pipework and Underground Foul Drainage
0.2NI-wide·Technical Booklet N Drainage
The guidance in Section 2 covers various aspects of sanitary pipework design including suitable materials, pipe sizing, capacity of pipes, seals and ventilation. Guidance is also given on drainage for
drainagenon-domesticdwellingPerformance Standards for Rainwater Drainage Systems
0.3NI-wide·Technical Booklet N Drainage
It is the view of the Department that the requirements of regulation 82 will be met if – (a) rainwater from a building is carried away from the surface by a drainage system; and (b) a rainwater draina
drainagenon-domesticdwellingGuidance on Rainwater Drainage Design
0.4NI-wide·Technical Booklet N Drainage
Section 4 gives guidance on the design of rainwater drainage including suitable materials, the sizing of pipes, gutters and outlets, and the capacity of the system related to the expected flow and the
drainagenon-domesticdwellingScope of Guidance
1.2NI-wide·Technical Booklet N Drainage
The provisions in this Technical Booklet are applicable primarily to domestic buildings and small non-domestic buildings. For larger or more complex systems seek specialist advice.
drainagedwellingnon-domesticMaterials for pipes, fittings and joints
2.1NI-wide·Technical Booklet N Drainage
The materials for sanitary pipework should be in accordance with the relevant standard given in Table 2.1. Where different metals are used they should be separated by non-metallic material to prevent
drainagenon-domesticCapacity of pipes
2.2NI-wide·Technical Booklet N Drainage
The capacity of a sanitary pipework system should be adequate to carry the expected flow at any point, provided that where a minimum size of pipe is stated in a paragraph, Table or Diagram that size o
drainagenon-domesticTable 2.1 Materials for sanitary pipework
Table 2.1NI-wide·Technical Booklet N Drainage
Material Relevant standard Pipes: Cast iron BS 416, BS EN 877 Copper BS EN 1254 Galvanised steel BS EN 1057 uPVC BS 3868 Polypropylene BS 4514, BS EN 1329 Other plastic BS EN 1451 BS EN 1329, BS EN 14
drainagenon-domesticTable 2.2 Flow rates from appliances
Table 2.2NI-wide·Technical Booklet N Drainage
Appliance Flow rate (litres/sec) WC (9 litre cistern) 2.30 Washbasin 0.60 Spray tap basin 0.06 Sink 0.90 Bath 1.10 Shower 0.10 Automatic washing machine 0.70 Urinal (per person unit) 0.15
drainagenon-domesticOverflow pipes
2.7NI-wide·Technical Booklet N Drainage
Where an overflow pipe discharges to a branch pipe or a stack it should do so through a trap. In all other cases an overflow pipe should discharge in a visible location and should not cause dampness i
drainagenon-domesticdwellingBranch pipes - sizing, bends and junctions
2.8NI-wide·Technical Booklet N Drainage
A branch pipe should be at least the same diameter as the appliance trap and where it serves more than one appliance and is unvented, it should be of at least the diameter and gradient given in Table
drainagenon-domesticdwellingBranch pipe discharge from upper and ground storeys
2.9NI-wide·Technical Booklet N Drainage
The branch pipe from an appliance on a storey above the ground storey should discharge into another branch pipe or a discharge stack. An appliance on the ground storey may discharge into another branc
drainagenon-domesticdwellingCommon branch discharge pipes (unvented)
Table 2.4NI-wide·Technical Booklet N Drainage
Common branch discharge pipes (unvented) Appliance | Max number to be connected | Max length of branch (m) | Min size of pipe (mm) | Gradient limits (fall per metre) min (mm) | max (mm) WCs | 8 | 15
drainagenon-domesticdwellingRodding points for branch pipe access
2.10NI-wide·Technical Booklet N Drainage
Rodding points should be provided to give access to any length of branch pipe which cannot be reached by removing a trap.
drainagenon-domesticdwellingBranch connections to stacks - height and spacing requirements
Diagram 2.1NI-wide·Technical Booklet N Drainage
Branch connections to stacks. Minimum height (H) requirements: houses up to 3 storeys 450 mm; any building up to 5 storeys 750 mm; any building up to 20 storeys 1 storey; any building over 20 storeys
drainagedwellingnon-domestichrbDischarge stacks - diameter and installation
2.14NI-wide·Technical Booklet N Drainage
A stack should discharge into a drain and be of at least the internal diameter given in Table 2.5. The diameter of a stack should not reduce in the direction of flow, nor have an offset in any part ca
drainagenon-domesticAccess for clearing blockages in stacks
2.17NI-wide·Technical Booklet N Drainage
Rodding points should be provided to give access to a length of stack or discharge stacks which cannot be reached from another part of the system.
drainagenon-domesticdwellingMaterials for pipes, fittings and joints
3.1NI-wide·Technical Booklet N Drainage
The materials for drains should be in accordance with the relevant standards given in Table 3.1. Where different metals are used they should be separated by non-metallic material to prevent electrolyt
drainagenon-domesticdwellingMaterial standards for underground foul drainage
Table 3.1NI-wide·Technical Booklet N Drainage
Material for underground foul drainage Material Relevant standard Rigid pipes: Fibre cement BS EN 588 Vitrified clay BS 65, BS EN 295 Concrete BS 5911, BS EN 1916, BS EN 1917, BS 437 Grey iron BS 437
drainagenon-domesticdwellingLayout of drainage system
3.2NI-wide·Technical Booklet N Drainage
The system should have as few changes of direction and gradient as practicable, and access points (see paragraph 3.12) should be provided at such changes. Drains should be laid to an even gradient and
drainagenon-domesticdwellingCapacity of pipes
3.3NI-wide·Technical Booklet N Drainage
The capacity of a system should be adequate to carry the expected peak flow at any point provided that the pipe diameter is not less than 100 mm where the drain carries water from a WC and 75 mm in al
drainagenon-domesticdwellingCombined systems capacity
3.4NI-wide·Technical Booklet N Drainage
The capacity of a system carrying both foul water and rainwater should be adequate for the combined peak flow. see para 3.3
drainagenon-domesticdwellingSiting of access points for drains
3.13NI-wide·Technical Booklet N Drainage
An access point should be provided at the following – (a) at or near the head of each length of drain; (b) at a bend; (c) at a change of gradient; (d) at a change of pipe size; (e) at a junction; (f)
drainagenon-domesticdwellingMinimum dimensions for access fittings and chambers
Table 3.4NI-wide·Technical Booklet N Drainage
Internal sizes Cover sizes Type Depth to invert (m) Length x width (mm x mm) Circular (mm) Length x width (mm x mm) Circular (mm) Rodding eye – As drain but minimum 100 – – – Access fitting: small lar
drainagenon-domesticdwellingConstruction of access points - General requirements
3.14NI-wide·Technical Booklet N Drainage
An access point should contain the foul water under working conditions, restrict the entry of ground water and rainwater, and be constructed of a material given in Table 3.6.
drainagenon-domesticDrain Watertightness Testing Requirements
3.15NI-wide·Technical Booklet N Drainage
A drain of diameter less than 300 mm should be capable of withstanding a test either – (a) by water to a pressure equal to 1.5 m head of water measured above the invert at the top of the drain; or (b)
drainagenon-domesticdwellingWater Test Procedure and Leakage Limits
3.15NI-wide·Technical Booklet N Drainage
A drain which is to be water tested should be divided into sections so that the head of water at the lower end of the section should not exceed 4 m. The section of drain should be filled, left standin
drainagenon-domesticdwellingGutter joints watertightness
4.7NI-wide·Technical Booklet N Drainage
Gutter joints should remain watertight under working conditions. A rainwater pipe inside a building should be capable of withstanding the test described in paragraph 2.4. A rainwater drain (other than
drainagenon-domesticdwellingBritish Standards for Drainage Materials and Systems
Appendix Publications referred toNI-wide·Technical Booklet N Drainage
British Standards BS EN ISO 12944: Parts 1 to 8 Paints and varnish. Corrosion protection of steel structures by protective paint systems. BS EN ISO 14713: 1999 Zinc coatings. Guidance and recommendati
drainagenon-domesticdwellingReferenced British Standards for Drainage Materials and Systems
NI-wide·Technical Booklet N Drainage
BS EN 1254-1: 1998 Copper and copper alloys. Plumbing fittings: Part 1: Fittings with ends for capillary soldering or capillary brazing to copper tubes. Incorporating Amendment: AMD 10099 July 1998. P
drainagenon-domesticdwellingReferenced British and European Standards for Drainage Systems
NI-wide·Technical Booklet N Drainage
BS EN 12200-1: 2000 Plastics rainwater piping systems for above ground external use – unplasticized poly (vinyl chloride) (PVC-U): Part 1: Specifications for pipes, fittings and the system. BS EN 123
drainagenon-domesticdwelling