Technical Booklet N Drainage·Page 28·3.15

Water Test Procedure and Leakage Limits

Water testing procedures require dividing drains into sections with specific head limits, standing times, and maximum acceptable leakage rates measured in litres per metre diameter per metre run.

A drain which is to be water tested should be divided into sections so that the head of water at the lower end of the section should not exceed 4 m. The section of drain should be filled, left standing for 2 hours, topped up and the leakage measured after a further 30 minutes. The leakage during the 30 minute test period should not exceed 0.5 litres per meter diameter of pipe per metre run. For example – (a) for a 100 mm drain – 0.05 litres per metre run of drain (a drop of 6.4 mm per metre run); or (b) for a 150 mm drain – 0.08 litres per metre run of drain (a drop of 4.5 mm per metre run).