Technical Booklet L Combustion Appliances and Fuel Storage Systems·Page 93·D.1, D.2

Location and support of LPG cylinders

Guidance on positioning LPG cylinders with a combined capacity greater than 150 litres, including placement outside buildings with specified minimum distances from openings, heat sources, and drains.

D.1 The advice given in paragraph D.2 and Diagram D1 is informative and may be considered for an LPG storage installation that consists of a set of two or more cylinders having a combined capacity greater than 150 litres. D.2 A cylinder should stand upright, be secured by straps or chains against a wall outside the building in a well ventilated position at ground level. It should be readily accessible, reasonably protected from physical damage and located where it does not obstruct exit routes from the building. A firm level base, such as concrete not less than 50 mm thick or paving slabs bedded on mortar should be provided. The cylinder valves should be not less than - (a) 1000 mm horizontally and 300 mm vertically from openings in the building or heat sources such as flue terminals and tumble-dryer vents; and (b) 2000 mm horizontally from drains without traps, unsealed gullies and cellar hatches, unless an intervening wall not less than 250 mm high is provided.