Technical Booklet R Access to and Use of Buildings·Page 72·9.4

Width of horizontal circulation routes

Horizontal circulation routes within common areas must be level or ramped with an unobstructed width of not less than 1200 mm, or 1000 mm where a handrail is provided.

A horizontal circulation route within a common area should be level or ramped and have an unobstructed width of not less than 1200 mm. Where a handrail is provided, the width at handrail level may be reduced to not less than 1000 mm.