Technical Booklet P Sanitary Appliances Unvented Hot Water Storage and Scalding·Page 14·2.10

Thermal cut-out wiring for indirectly heated systems

Non self-resetting thermal cut-outs in indirectly heated systems must be wired to an approved motorised valve or device capable of shutting off flow to the primary heater, or alternatively the cut-out may be located on an incorporated boiler.

Where the system is indirectly heated the non self-resetting thermal cut-out should be wired to a motorised valve or some other device which is – (a) approved by a member of EOTA; or (b) approved by a body having NACCB accreditation, as being capable of shutting off the flow to the primary heater. However, an indirectly heated system, which incorporates a boiler, may have the thermal cut-out on the boiler.