Technical Booklet N Drainage·Page 21·3.5
Ventilation of drains and branch drains
Main drains and branch drains longer than 10 m must be ventilated using a ventilation stack, ventilated discharge stack, or separate ventilation pipe. A separate ventilation pipe must terminate either at least 900 mm above building openings within 3 m with an unobstructed cage or cover, or use an air admittance valve complying with BS EN standards.
The system should be ventilated at or near the head of a main drain, and a branch drain longer than 10 m. A ventilation stack (see paragraph 2.13) or, a ventilated discharge stack (see paragraph 2.15) or a separate ventilation pipe should be used. Where a separate ventilation pipe is used it should terminate either – (a) in the external air at least 900 mm above any opening into a building within 3 m, with a cage or cover which does not restrict the air flow (see Diagram 2.3); or (b) with an air admittance valve which complies with BS EN 12056: Part 2 and BS EN 12380.