Technical Booklet N Drainage·Page 15·2.11

Branch ventilating pipes

Branch ventilating pipes must be connected to branch pipes within 300mm of the trap and sized according to pipe length and bends, with specific termination and connection requirements.

Subject to paragraph 2.12 a branch ventilating pipe should be connected to a branch pipe within 300 mm of the trap (see Diagram 2.4) and should be not less than 25 mm diameter or, where the length of the ventilating pipe exceeds 15 m or has more than 5 bends, not less than 32 mm diameter. A branch ventilating pipe should – (a) terminate in the external air at least 900 mm above any opening into a building within 3 m, with a cage or cover which does not restrict the air flow (see Diagram 2.3); (b) connect to a ventilated discharge stack above the "spillover" level of the highest appliance served (see Diagram 2.4); or (c) connect to a ventilating stack (see paragraph 2.13).