Technical Booklet L Combustion Appliances and Fuel Storage Systems·Page 94·Appendix E
Referenced British Standards for Combustion Appliances and Fuel Storage Systems
This appendix lists the relevant British Standards and European Standards that apply to the design, testing, installation and safety of combustion appliances, chimneys, flue systems, and heating fuels covered by Technical Booklet L.
BS EN ISO 1182: 2002 Reaction to fire tests for building products – Non-combustibility test.
BS EN ISO 1716: 2002 Reaction to fire tests for building products – Determination of heat of combustion.
BS EN 303: Heating boilers.
Part 1: 1999 Heating bolier with forced draught burners. Terminology, general requirements, testing and marking. AMD 16720
BS EN 449: 2002+A1: 2007 Specification for Dedicated Liquified Petroleum Gas Appliances. Domestic Flueless Space Heaters (Including Diffusive Catalytic Combustion Heaters).
BS EN 1443: 2003 Chimneys. General Requirements.
BS EN 1457: 1999 Chimneys. Clay/Ceramic Flue Liners. Requirements and Test Methods. AMD 14077.
BS EN 1806: 2006 Chimneys. Clay/Ceramic Flue Blocks for Single Wall Chimneys. Requirements and Test Methods.
BS EN 1856: Chimneys. Requirements for metal chimneys.
Part 1: 2009 System chimney products.
Part 2: 2009 Metal liners and connecting flue pipes.
BS EN 1857: 2010 Chimneys. Components. Concrete Flue Liners.
BS EN 1858: 2008 Chimneys. Components. Concrete flue blocks.
BS EN 13141: 2004 Ventilation for buildings. Performance testing of components/products for residential ventilation. Externally and internally mounted air transfer devices.
BS EN 13384: 1: 2002+A1:2008 Chimneys. Thermal and fluid dynamic calculation methods. Chimneys serving one appliance.
BS EN 13501 Fire classification of construction products and building elements.
Part 1: 2007 +A1: 2008 Classification using test data from reaction to fire tests.
BS EN 13502: 2002 Chimneys. Requirements and test methods for clay/ceramic flue terminals.
BS EN 14213: 2003 Heating fuels. Fatty acid methyl esters (FAME). Requirements and test methods.