Technical Booklet L Combustion Appliances and Fuel Storage Systems·Page 90·B.8
Pressure classes
Pressure classes designate how chimneys operate and their gas-tightness requirements. Classes N, P, and H with numeric suffixes 1 or 2 indicate natural draught, positive pressure, and high-pressure applications respectively, with lower numbers being more onerous.
Pressure classes are set out in Table B2 and expressed as either 'N', 'P' or 'H' followed by either '1' or '2'. N relates in general to natural draught chimneys i.e. operating under negative pressure where the value 1 or 2 allows for a different class of product; metal chimneys to BS EN 1856: 1 have the class N1. In the UK the value N2 should be assigned as a minimum to masonry chimneys. P and H relate to chimneys which operate under positive pressure e.g. for fan assisted applications and diesel generators respectively. The pressure designation depends on the gas-tightness it achieves, the lower number being the more onerous, the higher allowed leakage for positive pressure application being intended to external installations.