Technical Booklet L Combustion Appliances and Fuel Storage Systems·Page 56·4.9

Example calculation of free area of air vent for open-flued boiler

Demonstrates the method for calculating cooling air and combustion air vent areas for a 15 kW open-flued boiler using Diagram 4.2 methodology.

An open-flued boiler with a rated input of 15 kW (net) is installed in an appliance compartment such as a boiler room, which is ventilated directly to the outside. The design of the boiler is such that it requires cooling air. In these circumstances – The cooling air is exhausted via vent D, which has an area of – 15 x 500 = 7500 mm2 The cooling air and the air needed for combustion and the safe operation of the flue enters via vent E, which has an area of – 15 x 1000 = 15000 mm2