Technical Booklet L Combustion Appliances and Fuel Storage Systems·Page 51·Table 3.5

Minimum thickness of components for prefabricated appliance chambers

Prefabricated appliance chamber components must meet specified minimum thickness requirements: base 50 mm, side sections 75 mm, back section 100 mm, and top slab/lintel/gather 100 mm.

Table 3.5 Minimum thickness of components for prefabricated appliance chambers Component | Minimum thickness (mm) Base | 50 Side section, forming wall on either side of chamber | 75 Back section, forming rear chamber | 100 Top slab, lintel or gather, forming top of chamber recess | 100