Technical Booklet L Combustion Appliances and Fuel Storage Systems·Page 41·Table 3.3

Flue outlet positions for solid fuel appliances

Table 3.3 specifies minimum clearances and horizontal distances for flue outlets depending on their location relative to the ridge, roof, openings, and adjoining buildings.

Table 3.3 Flue outlet positions for solid fuel appliances Item 1 - At or within 600 mm of the ridge: Not less than 600 mm above the ridge. Item 2 - Elsewhere on a roof, whether pitched or flat: Not less than 2300 mm horizontally from the nearest point on the weather surface; and (a) not less than 1000 mm above the highest point of intersection of the flue/chimney and the weather surface; or (b) not less than as high as the ridge. Item 3 - Below (on a pitched roof) or within 2300 mm horizontally to an openable rooflight, dormer window or other opening: Not less than 1000 mm above the top of the opening. Item 4 - Within 2300 mm of an adjoining building, whether or not beyond the boundary: Not less than 600 mm above the adjacent building. Notes: (1) The weather surface is the building external surface, such as its roof, tiles or external walls. (2) A flat roof has a pitch less than 10°. (3) The clearances given for items 1 and 2, as appropriate, should also apply.