Technical Booklet L Combustion Appliances and Fuel Storage Systems·Page 38·Table 3.1 Notes

Air supply notes and exceptions

Notes provide guidance on extract fans in solid fuel appliance rooms, alternative air supply requirements for simple open fires, and assumptions for dwelling air permeability when not determined.

Notes: (1) Extract fans should not be installed in the same room or space as a solid fuel burning appliance, see paragraph 2.17. (2) For simple open fires as depicted in Diagram 3.12 the air supply requirement can be met with room ventilation areas as follows - Nominal fireplace opening size 500 mm 450 mm 400 mm 350 mm | Total equivalent area of permanently open air vents 20500 mm2 18500 mm2 16500 mm2 14500 mm2 (3) A dwelling constructed prior to 2008 should not normally have an air permeability of less than 5.0 m3/(h.m2) at 50 Pa unless extensive measures have been taken to improve air tightness, see Appendix C. When it is not possible to determine if the air permeability of a dwelling is likely to be more than 5.0 m3/(h.m2) then it should be assumed that the dwelling has an air permeability of 5.0 m3/(h.m2) or less.