Technical Booklet K Ventilation·Page 46·Table 3.2
Whole building ventilation rate for air supply to offices
Table specifying minimum outdoor air supply rates for offices and extract rates for specific room types including those with printers, photocopiers, sanitary accommodation, washrooms, and food preparation areas.
Table 3.2 Whole building ventilation rate for air supply to offices
Air supply rate
Total outdoor air supply rate for offices (no smoking and no significant pollutant sources): 10 l/s per person
Room Extract rate
Rooms containing printers and photocopiers in substantial use (greater than 30 minutes per hour): Air extract of 20 l/s per machine during use. Note that, if the operators are in the room continuously, use the greater of the extract and whole building ventilation rates
Office sanitary accommodation and washrooms: Intermittent air extract rate of – 15 l/s per shower/bath, 6 l/s per WC/urinal
Food preparation areas (not for commercial kitchens): Intermittent air extract rate of – 15 l/s with microwave, 30 l/s adjacent to the hob with cooker(s), 60 l/s elsewhere with cooker(s). All to operate while food preparation is in progress
Specialist buildings/spaces (e.g. commercial kitchens, sports centres): See paragraph 3.30 to 3.58
Note: Adjacent to a hob means either – (a) incorporated within a cooker hood located over the hob; or (b) located near the ceiling within 300 mm of the centre line of the space for the hob.