Technical Booklet H Stairs Ramps Guarding and Protection from Impact·Page 37·Table 4.1

Table 4.1 - Maximum length and rise of ramps

This table specifies the maximum ramp length in metres and maximum rise in millimetres for each gradient ratio from 1:20 to 1:12.

Table 4.1 Maximum length and rise of ramps Gradient of ramp | Maximum length of ramp (m) | Maximum rise of ramp (mm) 1:20 | 10 | 500 1:19 | 9 | 474 1:18 | 8 | 444 1:17 | 7 | 412 1:16 | 6 | 375 1:15 | 5 | 333 1:14 | 4 | 286 1:13 | 3 | 231 1:12 | 2 | 166