Technical Booklet H Stairs Ramps Guarding and Protection from Impact·Page 23·Table 3.1

Rise and Going Dimensions by Stair Category

Table specifying minimum and maximum rise and going dimensions for private stairs, common stairs in blocks of dwellings, and stairs in other buildings.

Table 3.1 Rise and going Category | Rise minimum (mm) | Rise maximum (mm) | Going minimum (mm) | Going maximum (mm) Private stair | 75 | 220* | 220* | 220* A common stair in a block of dwellings | 75 | 170 | 250 | 250 A stair in any building (other than a private stair or a common stair in a block of dwellings) | 150 | 170 | 250 | 250 Note: A stair within more than one category should be constructed to the more onerous standard. *see also paragraph 3.12.