Technical Booklet G Resistance to the Passage of Sound·Page 108·6.14

Solid masonry separating wall - ceiling void and roof space junction

A solid masonry type 1 separating wall need not extend continuously to the underside of the structural floor or roof if a double-layer plasterboard ceiling with mineral wool in the roof void is provided, provided the ceiling is not perforated and joists and sheets are not continuous between residential rooms.

In the case of the junction between a solid masonry separating wall type 1 and the ceiling void and roof space, the solid wall need not be continuous to the underside of the structural floor or roof provided that – (a) there is a ceiling consisting of two or more layers of plasterboard, of minimum total mass per unit area 20 kg/m2; (b) there is a layer of mineral wool (minimum thickness 200 mm, minimum density 10 kg/m3) in the roof void; and (c) the ceiling is not perforated. The ceiling joists and plasterboard sheets should not be continuous between rooms for residential purposes (see Diagram 6.1).

Source — /Users/richardhill/Documents/planning-arch-project/data/documents/regional/Technical Booklet G - Resistance to the Passage of Sound.pdf