Technical Booklet G Resistance to the Passage of Sound·Page 97·4.32
Floor treatment 2 – platform floor with absorbent material: Construction specification
This treatment uses mineral wool in the floor cavity and a floating layer of board material on a resilient layer to improve an existing timber floor's sound resistance. Specific minimum thicknesses, densities, and mass requirements must be met.
Where this treatment is used to improve an existing timber floor, a layer of mineral wool (minimum thickness 100 mm, minimum density 10 kg/m3) should be laid between the joists in the floor cavity.
The floating layer should be –
a minimum of two layers of board material;
minimum total mass per unit area 25 kg/m2;
each layer of minimum thickness 8 mm; and
fixed together (e.g. spot bonded or glued/screwed) with joints staggered.
The floating layer should be laid loose on a resilient layer.
The resilient layer specification is –
mineral wool, minimum thickness 25 mm, density 60 to 100 kg/m3; and
the mineral wool may be paper faced on the underside.
Note – The lower figure of density for the resilient layer gives the best insulation but a "softer" floor. In such cases additional support can be provided around the perimeter of the floor by using a timber batten with a foam strip along the top attached to the wall.