Technical Booklet G Resistance to the Passage of Sound·Page 79·3.69
Cavity wall closure requirements for floor type 2
External cavity walls must have the cavity closed with a cavity stop ensuring adequate drainage, unless the cavity is fully filled with mineral wool or expanded polystyrene beads.
Where the external wall is a cavity wall –
(a) the outer leaf of the wall may be of any construction; and
(b) the cavity should be closed with a cavity stop (see Diagram 3.16) ensuring adequate drainage, unless the cavity is fully filled with mineral wool or expanded polystyrene beads (seek manufacturer's advice for other suitable materials).