Technical Booklet G Resistance to the Passage of Sound·Page 29·2.19
Tie type A for masonry cavity walls
Wire butterfly ties or ties with specified dynamic stiffness must be used to connect cavity masonry wall leaves, limited to cavity widths of 50-75 mm with minimum 90 mm masonry leaf thickness, or calculated according to dynamic stiffness formula n.kXmm<4.8 MN/m3.
Connect the leaves of a cavity masonry wall only where necessary by wire type (butterfly) ties as described in BS EN 845-1 and spaced as required for structural purposes, see BS 5628-3 which limits this tie type and spacing to cavity widths of 50 mm to 75 mm with a minimum masonry leaf thickness of 90 mm. Alternatively, use wall ties with an appropriate measured dynamic stiffness for the cavity width. The specification for wall ties of dynamic stiffness, kXmm in MN/m with a cavity width of X mm and n ties/m2 is n.kXmm<4.8 MN/m3.