Technical Booklet F2 Conservation of Fuel and Power in Buildings Other Than Dwellings·Page 37·2.65

Controls for Heating, Ventilation and Air Conditioning Systems

Building service systems must be divided into separate control zones with independent timing and temperature control, preventing simultaneous heating and cooling operation, with central plant operating only when zone systems require it.

The following provisions should be made for heating, ventilation and air conditioning system controls – (a) the fixed building services system(s) should be subdivided into separate control zones to correspond to each area of the building that has a significantly different solar exposure, or occupancy period or type of use; (b) each separate control zone should be capable of independent timing and temperature control and, where appropriate, ventilation and air circulation rate; (c) the service should respond to the requirements of the space it serves. Where both heating and cooling are provided, they should be controlled so as not to operate simultaneously; and (d) central plant should operate only as and when the zone systems require it. The default condition should be "off".