Technical Booklet F1 Conservation of Fuel and Power in Dwellings·Page 17
Dwelling Type Definition for Air Tightness Testing
Defines criteria for classifying dwellings as the same type for air tightness testing purposes, requiring matching generic form, storeys, design air permeability, adjacency to unheated spaces, construction details, penetrations, and envelope areas.
Dwelling type – for the purposes of air tightness testing, is the allocation of each dwelling on a development to a generic dwelling type by the person carrying out the air tightness testing. To be classed as of the same dwelling type the dwelling should comply with all of the following –
(a) be of the same generic form (i.e. detached, semi-detached, end terrace, mid-terrace, ground floor flat (inc. ground floor maisonette), mid-floor flat, top-floor flat (inc. top-floor maisonette));
(b) be of the same number of storeys;
(c) be of the same design air permeability;
(d) have similar adjacency to unheated spaces such as stairwells, integral garages, etc.;
(e) have the same principal construction details (as identified by Accredited Construction Details or bespoke construction detail reference codes);
(f) have a similar (±1) total number of significant penetrations, (i.e. windows, doors, flues/chimneys, supply/exhaust terminals and waste water pipes); and
(g) have envelope areas that do not differ by more than 10%.