Technical Booklet E Fire Safety·Page 167·6.14
Natural venting requirements for basement smoke outlets
Basement storeys may be ventilated by smoke outlets that must be ceiling-level, provide 2.5% aggregate free area of the floor space, be evenly distributed around the perimeter, not obstruct escape routes, and be labelled.
A basement storey may be ventilated by smoke outlets which should –
(a) be sited at ceiling level within the space they serve;
(b) have an aggregate free area of not less than 2.5% of the floor area of the space they serve;
(c) be distributed as evenly as possible around the perimeter of the building;
(d) be located so that they do not adversely affect any escape route from the building; and
(e) have a sign stating "smoke outlet from basement" fixed adjacent to each external outlet point.
The smoke outlets from a place of special fire hazard should be separate from the smoke outlets from other areas.