Technical Booklet E Fire Safety·Page 166·6.12

Basement venting facility requirements

Venting facilities connected directly to external air must be provided from every basement storey except those in Purpose Group 1(b) or (c), small basements under 200 m², shallow basements under 3 m deep, car parks with compliant ventilation, or strong rooms.

Venting facilities, connected directly to the external air, should be provided from every basement storey other than – (a) a basement in a building of Purpose Group 1(b) or (c); (b) a basement storey which – (i) has a floor area not more than 200 m²; or (ii) has a floor not more than 3 m below the lowest adjacent ground level; (c) a basement storey used for car parking and ventilated in accordance with paragraph 4.50; and (d) a basement storey or that part of a basement storey used as a strong room.

Source — /Users/richardhill/Documents/planning-arch-project/data/documents/regional/Technical Booklet E - Fire Safety.pdf