Technical Booklet E Fire Safety·Page 163·6.4
Minimum number of firefighting shafts by floor area
The minimum number of firefighting shafts required depends on whether the building has sprinkler protection and the floor area of the largest storey, with reference to BS 5306-2 or BS EN 12845 standards.
Where a building is to be provided with firefighting shafts the minimum number (subject to paragraph 6.5) should be – (a) where a building is fitted throughout with an automatic sprinkler system complying with the relevant recommendations of BS 5306-2 or BS EN 12845 as given in Table 6.1 for the appropriate floor area; or (b) where a building is not fitted throughout with such a sprinkler system – at least one for every 900 m2, (or part thereof) of floor area of the largest storey given in paragraph 6.3(a) to (d) as appropriate.