Technical Booklet E Fire Safety·Page 159·Diagram 5.6

Limitation on areas and spacing of certain thermoplastic rooflights

Thermoplastic rooflights must not exceed 5 m² in area and must be spaced at least 3 m apart in any direction, with exceptions for certain classified rooflights in non-residential buildings that may be spaced 1.8 m apart if evenly distributed and not exceeding 20% of floor area.

Limitation on areas and spacing of certain thermoplastic rooflights rooflight max. area 5 m² 3 m minimum between any two rooflights in any direction Notes: Or group of rooflights amounting to not more than 5 m². Class 3 (National class) or Class D-s3,d2 (European class) rooflights to rooms in non-residential purpose groups may be spaced 1.8 m apart provided that the rooflights are evenly distributed and do not exceed 20% of the floor area of the room. 1 Surrounding roof covering to be a material of limited combustibility for at least 3 m distance. 2 Where paragraph 4.21(a) applies rooflights should be not less than 1.5 m from the compartment wall.