Technical Booklet E Fire Safety·Page 148·Table 5.4
Permitted unprotected percentages in relation to enclosing rectangles (Method 3) for 18 m high buildings
Table specifying minimum boundary distances in metres required based on the width of the enclosing rectangle and the permitted unprotected percentage of the facade for 18 m high buildings. Figures in brackets apply to Purpose Groups 1, 2, 3, 5 and 7(b).
Enclosing rectangle 18 m high
Width of enclosing rectangle (m): 3, 6, 9, 12, 15, 18, 21, 24, 27, 30, 40, 50, 60, 80, 100, 120, No limit
Distance from relevant boundary for unprotected percentage not exceeding: 20%, 30%, 40%, 50%, 60%, 70%, 80%, 90%, 100%
Minimum boundary distance (m) – figures in brackets are for Purpose Groups 1, 2, 3, 5 and 7(b):
3 m: 2.0(1.0), 2.5(1.5), 3.5(2.0), 4.0(2.5), 5.0(2.5), 5.0(3.0), 6.0(3.5), 6.5(4.0), 6.5(4.0)
6 m: 3.5(1.5), 4.5(2.5), 5.5(3.5), 6.5(4.0), 7.5(4.5), 8.0(5.0), 9.0(5.5), 9.5(6.0), 10.0(6.5)
9 m: 4.5(2.0), 6.0(3.5), 7.0(4.5), 8.5(5.0), 9.5(6.0), 10.0(6.5), 11.0(7.0), 12.0(8.0), 12.5(8.5)
12 m: 5.0(2.5), 7.0(4.0), 8.5(5.0), 10.0(6.0), 11.0(7.0), 12.0(7.5), 13.0(8.5), 14.0(9.0), 14.5(10.0)
15 m: 6.0(2.5), 8.0(4.5), 9.5(6.0), 11.0(7.0), 12.5(8.0), 13.5(8.5), 14.5(9.5), 15.5(10.5), 16.5(11.0)
18 m: 6.5(2.5), 8.5(5.0), 11.0(6.5), 12.0(7.5), 13.5(8.5), 14.5(9.5), 16.0(11.0), 17.0(11.5), 18.0(13.0)
21 m: 7.0(3.0), 9.5(5.5), 11.5(7.0), 13.0(8.0), 14.5(9.5), 16.0(10.5), 17.0(11.5), 18.0(12.5), 19.5(13.0)
24 m: 7.5(3.0), 10.0(5.5), 12.0(7.5), 14.0(8.5), 15.5(10.0), 16.5(11.0), 18.5(12.0), 19.5(13.0), 20.5(14.0)
27 m: 8.0(3.5), 10.5(6.0), 12.5(8.0), 14.5(9.0), 16.5(10.5), 17.5(11.5), 19.5(12.5), 20.5(13.5), 21.5(14.5)
30 m: 8.0(3.5), 11.0(6.5), 13.5(8.0), 15.5(9.5), 17.0(11.0), 18.5(12.0), 20.5(13.5), 21.5(14.5), 22.5(15.5)
40 m: 9.0(4.0), 12.0(7.0), 15.0(9.0), 17.5(11.0), 19.5(12.0), 21.5(13.5), 23.5(15.0), 25.0(16.5), 26.0(17.5)
50 m: 9.5(4.0), 13.0(7.0), 16.5(9.5), 19.0(11.5), 21.5(13.0), 23.5(15.0), 26.0(16.5), 27.5(18.0), 29.0(19.0)
60 m: 10.0(4.0), 14.0(7.5), 17.5(10.0), 20.5(12.0), 23.0(14.0), 26.0(16.0), 27.5(17.5), 29.5(19.5), 31.0(20.5)
80 m: 10.0(4.0), 15.0(7.5), 19.0(10.0), 22.5(13.0), 26.0(15.0), 28.5(17.0), 31.0(19.0), 33.5(21.0), 35.0(22.5)
100 m: 10.0(4.0), 16.0(7.5), 20.5(10.0), 24.0(13.5), 28.0(16.0), 31.0(18.0), 33.5(20.5), 36.0(22.5), 38.5(24.0)
120 m: 10.0(4.0), 16.5(7.5), 21.0(10.0), 25.5(14.0), 29.5(16.5), 32.5(19.0), 35.5(21.0), 39.0(23.5), 41.5(25.5)
No limit: 10.0(4.0), 17.0(8.0), 22.0(10.0), 26.5(14.0), 30.5(17.0), 34.0(19.5), 37.0(22.0), 41.0(24.0), 43.5(26.5)