Technical Booklet E Fire Safety·Page 140·5.9
Relevant Boundary Definition and Requirements
A relevant boundary must coincide with, be parallel to, or be at an angle of not more than 80° to the side of the building. It can be the actual premises boundary, the centre line of a road/river/canal/railway, or a notional boundary between two or more buildings where at least one is Purpose Group 1, 2, or 5.
For a boundary to be a relevant boundary it should coincide with, be parallel to or be at an angle of not more than 80° to the side of the building (see Diagram 5.2).
A relevant boundary may be –
(a) the actual boundary of the premises on which the building is located;
(b) the centre line of a road, river, canal or railway which adjoins the actual boundary; or
(c) a notional boundary established where two or more buildings (one of which is of Purpose Group 1, 2 or 5) are to share the same site. A notional boundary should be assumed so that both buildings comply with the space separation distances required by this Section.
Where a notional boundary is to be established and one of the buildings is an existing building, that building should be treated as if it were a new building.