Technical Booklet E Fire Safety·Page 139·5.6
Assumptions for space separation calculations
Space separation provisions are based on specific assumptions about fire compartmentalisation, fire intensity related to building use and sprinklers, identical opposing elevations at equal distances, and radiation from fire-resisting external walls.
The assumptions for establishing space separation are –
(a) that the fire will involve a complete compartment but will not spread to other compartments;
(b) that the intensity of a fire is related to the use of the building and will be moderated by a sprinkler system where it is provided;
(c) that a building, which has an identical elevation, is located on the opposite side of, and at the same distance from, the relevant boundary; and
(d) that radiation from that part of the external wall, which has the fire resistance required by Section 4, is discounted unless its external surface is combustible as described in paragraph 5.10.