Technical Booklet E Fire Safety·Page 135·5.4B

Cavity Surfaces in External Wall Construction

For external wall construction of buildings with masonry or concrete inner leaf cladding systems, cavity-facing surfaces must meet Table 5.1A provisions and Section 4 cavity barrier requirements, unless Regulation 23(2) applies.

In the case of an external wall construction, of a building which, by virtue of paragraph 4.40(d) (external cladding system with a masonry or concrete inner leaf), is not subject to the provisions of Table 4.7, the surfaces which face into cavities should also meet the provisions of Table 5.1A, and provisions for cavity barriers in Section 4, but where Regulation 23(2) applies, that regulation prevails over guidance provided in Table 5.1A and Section 4.