Technical Booklet E Fire Safety·Page 127·4.51
Ventilation for non-open-sided car parks
Car parks that do not meet open-sided criteria must have either natural ventilation with permanent openings of at least 2.5% of floor area with cross-ventilation, or ceiling vents with equivalent permanent opening area and through-flow arrangement.
Where a car park does not comply with the provisions of paragraph 4.50 it should not be regarded as open-sided for the purposes of Table 4.2 [i.e. it falls in Purpose Group 7(b)(ii)]. However, there is a need for ventilation in such a car park, therefore in addition to the provisions of paragraph 4.49 it should have either –
(a) natural ventilation at each storey –
(i) by permanent openings at each car parking level, having an aggregate ventilation area of not less than 2.5% of the floor area at that level, with not less than half that ventilation area equally divided in two opposing walls and distributed to provide effective cross-ventilation; or
(ii) by suitable vents at ceiling level on each car parking level having an aggregate area of permanent opening not less than 2.5% of the floor area and so arranged as to have a through flow of air; or
Source — /Users/richardhill/Documents/planning-arch-project/data/documents/regional/Technical Booklet E - Fire Safety.pdf