Technical Booklet E Fire Safety·Page 121·4.41

Cavity barriers in cavities over undivided rooms exceeding maximum dimensions

Sets out requirements for cavity barriers in cavities above rooms that exceed the maximum dimensions specified in Table 4.7, including conditions allowing reduced provision based on room size, compartmentation, fire detection, and material classifications.

Where the cavity is over an undivided room which – (a) exceeds the appropriate maximum dimension for a cavity in Table 4.7, cavity barriers need only be provided on the line of the enclosing walls of that room, provided that they are not more than 40 m apart and that the surfaces exposed in the cavity are not lower than Class 1 (National class) or Class C-s3,d2 (European class); or (b) exceeds 40 m (in either direction on plan), cavity barriers need not be provided where – (i) the room and the cavity together are compartmented from the rest of the building; (ii) an automatic fire detection and fire alarm system complying with BS 5839-1 is fitted in the building; (iii) the surface of the ceiling exposed in the cavity is of Class 0 (National class) or Class B-s3,d2 or higher (European class) and the ceiling supports and fixings in the cavity are of non-combustible construction; (iv) the surface spread of flame classification of any pipe insulation in the cavity is not lower than Class 1 (National class) or Class C-s3,d2 (European class); (v) any electrical wiring in the cavity is laid in metal trays or in metal conduit; (vi) any other material in the cavity is a material of limited combustibility; and