Technical Booklet E Fire Safety·Page 115·4.36

Provision of cavity barriers - general requirement

Cavity barriers must be provided to restrict smoke and flame spread through concealed spaces. They are required at intersections of fire-resisting construction with elements containing cavities, and at locations specified in Table 4.6 for each purpose group.

To restrict the spread of smoke and flame through concealed spaces in the construction of a building, cavity barriers should be provided – (a) in a building of any purpose group – (i) at the intersection of fire-resisting construction and an element containing a cavity as shown in Diagram 4.4; and (ii) as set out in Table 4.6 for the appropriate purpose group of the building and the specified locations. [Note – alternative arrangements for items 1, 3 and 4 are shown in Diagram 4.5 and for item 2 in Diagram 4.6. Notes (3) and (4) to Table 4.6 are supported by Diagrams 4.7 and 4.8 respectively]; and (b) in a building of Purpose Group 2, 3, 4, 5, 6 or 7 – so that the maximum dimension of a cavity, (other than one described in paragraph 4.40 or 4.41) should be not greater than that given in Table 4.7 for the appropriate location of the cavity.