Technical Booklet E Fire Safety·Page 109·4.26
Glazed screens in protected shafts
Glazing may be used between a protected shaft containing a stairway and an adjacent corridor or lobby, subject to conditions on shaft type, fire resistance, and glazing extent or corridor fire resistance.
Glazing may be incorporated in the wall between a protected shaft containing a stairway, and a corridor or lobby which gives access to that stairway provided that –
(a) the protected shaft is not a firefighting shaft;
(b) the protected shaft is not required to have more than 60 minutes fire resistance; and
(c) the glazing has not less than 30 minutes fire resistance in respect of integrity; and either –
(i) the glazing is limited in extent in accordance with Table 2.8; or
(ii) the corridor or lobby has not less than 30 minutes fire resistance (see Diagram 4.3).