Technical Booklet E Fire Safety·Page 109·4.23

Openings in compartment walls and floors

Compartment walls and floors should have no openings except for fire doors, pipes and ducts, waste chutes, atriums, or protected shafts meeting specified conditions.

A compartment wall (other than one described in paragraph 4.22) and a compartment floor should have no openings other than those – (a) having a fire-resisting self-closing door (see paragraph 4.29 to 4.35); (b) for the passage of pipes, ventilation ducts, chimneys, appliance ventilation duct or duct encasing one or more flue pipes – when the opening in the compartment wall or compartment floor should comply with paragraphs 4.43 to 4.47; (c) for a waste chute system constructed of non-combustible materials; (d) for an atrium designed in accordance with the relevant recommendations of BS 9999 BS 5588-7; and (e) for a protected shaft which complies with the provisions of paragraph 4.25 to 4.28.