Technical Booklet E Fire Safety·Page 108·Diagram 4.2 (b)

Junction of compartment wall and roof - Buildings Purpose Groups 1, 2(b), 3 or 5 up to 15 m

For buildings of Purpose Groups 1, 2(b), 3 or 5 not exceeding 15 m in height, compartment wall and roof junctions require mortar bedding, timber battens, sarking felt, and AA/AB/AC roof covering with fire-stopping extending 1.5 m each side and roof covering at least 375 mm.

AA, AB or AC roof covering 1.5 m 1.5 m mortar slates/tiles bedding timber battens sarking felt (b) Building of Purpose Group 1, 2(b), 3 or 5 not more than 15 m in height not less than 375 mm not less roof than 375 mm covering