Technical Booklet E Fire Safety·Page 105·4.19
Construction requirements for compartment walls and floors
Compartment walls and floors must form a complete fire barrier with appropriate fire resistance, and may incorporate timber elements if built into masonry or concrete with properly fire-stopped gaps. Walls separating buildings or separated parts must extend the full height in a continuous vertical plane.
Every compartment wall and compartment floor should –
(a) form a complete barrier to fire between the compartments they separate; and
(b) have the appropriate fire resistance required by paragraph 4.6.
A compartment wall may have timber beams, joists, purlins and rafters built into it provided that –
(i) the wall is of masonry or concrete construction;
(ii) any gaps between the wall and the timber are as small as practicable; and
(iii) any gaps are fire-stopped in accordance with paragraphs 4.46 and 4.47.
A compartment wall between two or more buildings should extend the full height of the buildings in a continuous vertical plane. Thus adjoining buildings should be separated only by walls and not by floors.
A compartment wall used to form a separated part of a building should extend the full height of the building in a continuous vertical plane. Thus separated parts should be separated only by walls and not by floors.