Technical Booklet E Fire Safety·Page 105·4.18
Compartmentation requirements by building purpose group
Sets out which walls and floors must act as compartment barriers in different types of buildings, including requirements for Purpose Groups 2-7 based on building type, occupancy divisions, compartment sizes, height, and basement depth.
(c) in a building of Purpose Group 2 –
(i) every floor; and
(ii) in the case of a health care building – a wall needed to divide a storey into compartments for means of escape purposes;
(d) in a building of Purpose Group 4, 6 or 7 a wall or floor provided to divide the building into different occupancies (i.e. ownership, tenancies or similar); and
(e) in a building of Purpose Group 3, 4, 5, 6, or 7 –
(i) a wall which is needed to subdivide a building, or separated part of a building, so that the maximum floor area or maximum volume, as appropriate, of a compartment given in Table 4.4 is not exceeded;
(ii) every floor in a building or a separated part of a building (other than the lowest floor) where that building or separated part has a floor at a height of more than 30 m above ground level;
(iii) the floor of the ground storey where a building or separated part of a building has one or more basements (with the exception of a small building described in paragraph 2.68); and
(iv) every basement floor in a building, or a separated part of a building (other than the lowest basement floor), where that building or separated part has a floor at a depth of more than 10 m below ground level.